Cables Connected in Parallel

08/11/2011 10:46 AM

If 2 conductors are connected in parallel, eg i6mmsq, 2No., to a breaker and serving a device, outlet, whatever.

and there is a difference in length between the two cables, what will be the effect, how serious will it be when the difference in length is very small?

what comes to mind is there will be unequal sharing of current, and the overall impedance will be affected.

anything more serious i should knw?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: Cables Connected in Parallel

08/11/2011 11:08 AM

Not a serious issue, But If smaller wire out of two can reach to breaker with out trouble, Then why not to cut longer one or make both equal, Equal means equal for practical purpose.Not the equal of an over killer.

What do you mean by very small? are you trying to control them in mm?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Cables Connected in Parallel

08/11/2011 12:40 PM

If you're talking 50/60Hz, I'd say it depends on total length of conductors and total difference in length.

Unless the difference is on the order of 10%, or more, I don't think it would matter.

Register to Reply
Anonymous Poster #1
#3

Re: Cables Connected in Parallel

08/11/2011 1:02 PM

Usually you are going to work at a current much lesser than their maximum capacity.

The Length is of course directly proportional to the impedance (with a bit of approximation) and Hence the currents sharing would be inversely proportional. So it would boil down to a sharing inequality a bit just less than the length inequality.

It really may not matter under normal circumstances. Afterall there are other things that may give rise to a bit of inequality too.

Register to Reply
Power-User

Join Date: Jan 2008
Posts: 127
Good Answers: 5
#4

Re: Cables Connected in Parallel

08/11/2011 10:55 PM

you shouldnt have any trouble but need to be aware that if you have doubled up the cable to meet current carrying capacity of the device and have a break\failure in one wire your other one will overheat causing you any number of problems and any circuit protection may not work due to undersized conductors.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Cables Connected in Parallel

08/12/2011 4:16 AM

It is more-or-less standard domestic electrical practice to run a ring circuit from a 32A breaker to a number of socket outlets using 2.5mm2 twin-and-earth cable for a floor area not exceeding 100m2, and this is covered in British Standard 7671. So there wouldn't appear to be an issue as it is hardly trail-blazing stuff.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8
In reply to #5

Re: Cables Connected in Parallel

08/16/2011 6:35 AM

"So there wouldn't appear to be an issue as it is hardly trail-blazing stuff".

It's been in use since 1942! And still going strong (until the EU mucks things up again).

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Apr 2009
Location: FL USA
Posts: 372
Good Answers: 9
#6

Re: Cables Connected in Parallel

08/12/2011 11:56 AM

As a current divider, each cable will carry it's share of the load proportionate to their individual resistance. R total = R1XR2/(R1+R2). If the length (resistance) difference is say 10% the sharing will be 10% more carried by the shorter (lower resistance) wire, assuming of course both wires are of the same gauge (conduction diameter).

__________________
What is right is not always popular. - What is popular is not always right.
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 69
#7

Re: Cables Connected in Parallel

08/12/2011 3:36 PM

The overall impedance will not change due to unequal sharing of current. But yes, the difference in length will result in an unequal amount of current through each cable since resistance is based on the length. However, this difference should be minimal if the difference in lengths are "very small".

__________________
The early bird may get the worm, but the second mouse get's the cheese.
Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#9

Re: Cables Connected in Parallel

08/18/2011 7:15 PM

This question will be understood better by doing home work by you. I will provide you the data and equation to do home work.

Cable size is mentioned 16mm2 which indicates you are using European cables and not American.

Let the distance between 220V source (Panel board) and load (Device-heater) be 50 meter. Load electrical data is 220V, 30Amps, 50Hz, 1-phase (Phase to Neutral) and unity power factor (pure resistive load or heater). Heater load is used here to minimize complex calculations due to unity power factor.

Owing to some reasons you got two 16mm2 cables of each lengths as 55meter(cable-1) and 60(cable-2). The two cables are connected in parallel to electrical source (Panel board) and Load (heater).

Electrical data of the cables from the cable manufacturer are as follows:

Cable-1(55meter) impedance: Z1 = 0.0792+j0.00728 Ohms

Cable-2(60meter) impedance: Z2 = 0.0864+j0.0079 Ohms

Cable -Ideal (50meter) impedance ZI = 0.072+j0.00662Ohms

To make further simplification, we use IEE code which advices to drop reactive Ohms up 16mm2 cable due to Resistance(R) value >10 *Reactance(X) value

Therefore cable impedance (Z) becomes as resistance(R) and as follows:

Z1=R1= 0.0792Ohms; Z2=R2= 0.0864Ohms; ZI=RI=0.072Ohms

Therefore the formulas are as given below and substitute above resistance values :

Effective impedance of the two unequal length parallel cables in Ohms= R1*R2/(R1+R2) ----1

In ideal case( two equal & exact length 50meters) effective impedance = RI/2 .......…2

By comparing Equation-1 and equation-2, you will get your answer. Similarly you can do other calculation such as current sharing, power loss in each cable and so and so forth.

I want to give you a practical advice that don't connect small size cables into parallel to load, if next higher size cables having double cross section is available. Always try to use single cable to load. In your case, it is better to use a cable size of 25mm2 or 35mm2 instead of 2*16mm2 and check which cable gives a. % voltage drop as acceptable to local code and b. cable current rating meets the load current.

Mushtaq Hussain-INDIA

__________________
B.E, M.I.E, M.S
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dcpppf (1); Grochy (1); lyn (1); Mushtaq Hussainh (1); PWSlack (1); rakesh_semwal (1); TonyS (1); U NO WHO (1)

Previous in Forum: REF Stability Testing for Delta/Star Transformer?   Next in Forum: Cable Tray

Advertisement