Difference Between Hard Wired Signal and Modbus

08/12/2011 8:10 AM

What is the main difference between a hard wired 20KV switchgear and another makin use of serial signal Modbus? Is it possible to connect fault signals to another panel(ECS) via modbus or must it be hard wired. I was told that only status display are suitable for modbus. Please enlighten me on this subject matter. What is the main advantage of the Modbus over hard wired signal?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Difference Between Hard Wired Signal and Modbus

08/12/2011 8:52 AM

I wouldn't trust ModBus with a protection systems. To prone to delay in transmitting signals. But others may know better. OK for indication and open/close signals.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#2

Re: Difference Between Hard Wired Signal and Modbus

08/12/2011 10:40 AM

MODBUS is a transmission protocol and can communicate via hardwire (serially) or wirelessly. You're getting your apples mixed in with your oranges. Here's a Wiki article for you.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
3
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Difference Between Hard Wired Signal and Modbus

08/13/2011 9:42 AM

The Modbus protocol is used extensively to 'read' data from 'slave' devices for reporting and historian purposes. Modbus can also 'write' data to slave devices, giving it control capability.

Modbus is a master/slave protocol where a slave is silent unless spoken to. The implication is that an alarm or an 'event' on a slave device is not broadcast via Modbus because there's no provision for a slave to talk unless first spoken to. Hence, the master has to poll the slave and get the slave's response in order to find out about the alarm or event. Depending on the application, whatever time that takes might or might not be a serious consideration.

The Modbus standard is not be considered deterministic, with fixed and known timing intervals.

An issue in Modbus is the absence of slave's response which ties up the Master until the time-out interval expires.

The transmission medium, the physical transport layer, is typically RS-232 for short distance (<10m) point-to-point, RS-485 for longer distances (<1000m) or ethernet, any of which have some susceptability to ground faults, lightning strikes and electrical noise. The robustness of the physical layer is solely up to the implementator, because there are no Modbus wiring components, like there are for Profibus, for example.

Modbus is an open protocol so its implementation is up to whomever implenments it. It has only recently in the last couple years had a compliance process, yet the protocol has been around for 30+ years.

I'm not familiar with the operational or safety issues of control of switchgear, but the selection of a control communications has to take into consideration the full range of comm's performance. There might well be conditions where hard-wired controls (I'll define that as on-off or analog signals to dedicated I/O points over copper wire) is necessary because either the physical transport or protocol limitations of Modbus are not appropriate for the task.

None of this detracts from the hundreds of thousands of Modbus installations that successfully do what they're supposed to, within the limitations of what Modbus does and how it does it. Many of these control implementations have hard-wired ESD circuits required by electrical code.

Register to Reply Good Answer (Score 3)