Transformer

08/14/2011 11:21 AM

HI friends

i have a building with total 400 kw load.

All instruments are of single phase.

So, what should be the transformer capacity ?

Register to Reply
Pathfinder Tags: calculating transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Dec 2009
Location: INDIA.
Posts: 39
#1

Re: tranformer

08/14/2011 11:35 AM

Use more than 400KW for better Transformer life..as standard transformer available in market.

__________________
"Keep work and family separate. "
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Tranformer

08/14/2011 11:45 AM

Since we don't know where you live it is impossible to give a meaningful answer.

Try giving more information.

The real answer is your local electrical code.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#3

Re: Tranformer

08/14/2011 11:45 AM

Please consider building expansion near future, say at 5 or 10 years estimated total load. In this you wont have to replace another transformer.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#4

Re: Tranformer

08/14/2011 2:39 PM

considering your load p.f to be o.8 (which is a practical value for residential single phase loads ), your apparent load will be : 400 /0.8 = 500KVA , so a transformer with 500KVA rating will be perfect for your present load. however you should buy a transformer with 20% extra capacity of 500KVA to account for any extra future load. so that means a transformer with capacity : 1.2 x 500 = 600 KVA . so buy a transformer of 600KVA rating.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Transformer

08/14/2011 3:35 PM

You need to perform an analysis of the instrument loads (starting current, operating current under load, etc) as well as an analysis of operating duty cycles (which equipment will be on when, etc).

If you cannot do this then get someone qualified to do it, no one here can possibly guess without a great deal more information, and even then.......

Is this a homework question?

__________________
jack of all trades
Register to Reply
Associate

Join Date: Jun 2007
Location: Sacramento, CA
Posts: 33
#6

Re: Tranformer

08/14/2011 4:02 PM

If this is a 1Φ load at 400kW, I'd consider switching to 3Φ. After 100kW it's <em>ALOT</> more efficient.

But as others have posted, we need more information here.

__________________
gisdude
Register to Reply Score 1 for Good Answer
Member

Join Date: Aug 2011
Posts: 7
#9
In reply to #6

Re: Tranformer

08/15/2011 10:49 AM

Hi!

My friend u r right but can u tell me the calculating formula ?

If my loads are of one distribution is of 89kw, second of 150 ,third of 161kw.

Now can u tell me my transformer's rating.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: Transformer

08/15/2011 2:44 AM

Rather than trying to calculate,fix a power analyser or data logger for at least 8hrs and record V,I,Hz, Var, W, pf, THD, max demand instantanous values of I,V etc and select the transformer size making allowance for future load.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#8

Re: Transformer

08/15/2011 3:22 AM

Hi Hitesh, if you know the KW Load, I have to presume that you also know your full load current, you will also know what your possible load changes are going to be in the next 10 years.

I hope your load is spread over 3 phase and by knowing the supply current per phase you can work out what you need for your existing supply and also plan what you would need for expansion over the next 5-10 years.

I hope this is of help

Cheers

Joe

The other suggestion (Just Joking) consult your local clairvoyant.

Register to Reply
Member

Join Date: Aug 2011
Posts: 7
#10
In reply to #8

Re: Transformer

08/15/2011 11:20 AM

Hi Joe,

your right but this is for my upcoming project and yet all instruments are not installed so that i don't know the current inspite of that wanna know the transformer rating to demand transformer from electrical co. cause it takes to long time in process.

I am already running with calculating 20% extra load.

This is my Hospitality project.

I can calculate app. current cause my approximate division of circuits are 1st of 89kw

2nd of 150kw & 3rd of 161kw.

Now can u tell me the calculating formula for this.

Regard,

Hitesh

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #10

Re: Transformer

08/15/2011 1:12 PM

If you have 3 circuits as described, and want to use a 3 phase supply transformer, then the transformer size will still be 400 kW.( Single phase or 3 phase).

89+150+161= 400 kW

The only thing that changes is the distribution panels ...

Register to Reply
Anonymous Poster #1
#12
In reply to #11

Re: Transformer

08/16/2011 2:11 AM

The transformer will ve in KVA and not KW.

OP had to tell the type of load (and the expected pf) even if we assume it to be about 0.8 it becomes 500KVA but then the loads (which may give the abnormal starting current requirements) , diversity factor etc would be needed for the sizing.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13
In reply to #12

Re: Transformer

08/16/2011 4:24 AM

Since the P.F. is not mentioned, and it seems that the load is made of INSTRUMENTS, the mentioning of kW will definitely trigger the question: what type of load etc, from the supplier so that he could specify the kVA.

In any case, I mentioned a p.f. of 0.8 and gave the kW rating for it. My answer is perfectly correct. The kVA can be deducted by removing the 0.8 from the formula. Specifying kW at o.8 p.f. is complete. (0.8 is standard p.f. for any power supplier)

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); coolyaar (1); GISdude (1); hitesh cahuhan (2); jack of all trades (1); Joe Sparky (1); LAA_Lucke (2); lyn (1); Noudge79 (1); pnaban (1); RAMAKANTA (1)