Interrupting Unit and Interrupter

08/15/2011 12:44 PM

Hello Technical Geeks!!

I am stuck at Circuitbreakers. Can you please tell me the difference between the number of interrupting chambers and number of interrupters?

"The circuit breaker operates as a single pressure puffer breaker with two interrupting chambers for each pole"

This statement is for a Gas Insulated Circuit Breaker. and I am damn sure that GIS has only one interrupter. So what do you mean by saying two interrupting chamber?

Here What does interrupting chamber indicate?

Also What is the difference between interrupting chamber and arcing chamber?

With Warm Regards,

ClassyLass

__________________
A.Classy.Lass
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Interrupting unit and interrpter

08/15/2011 1:13 PM

Perhaps you are only familiar with lower class high voltage switchgear. The dielectric strength of the interrupting medium has a finite limit, once that limit is reached multiple identical modules and/or chambers are used to in effect spread the interrupting duty over a greater dielectric/interrupting paths. You can think of a chamber as a subset of a module, where from one to N chambers comprise a module, N is dependent upon the interrupting duty placed on the module.

Googling gets lots of information, try this as a start http://www.hicoamerica.com/Files/HICO.GIS.pdf There are many others by the major manufacturers of GIS systems, simply look at the pictures to see how they are constructed.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Interrupting Unit and Interrupter

08/16/2011 10:22 AM

Also remember that GIS (Gas-Insulated Switchgear or Gas-Insulated Substation) is only one type of gas-insulated equipment. There are gas-insulated circuit breakers, circuit switchers, etc., and it is the manufacturer's decision how to design it to meet the standards and the operating requirements. Some might use a single interrupter, some might use multiple.

Even in GIS, just because you have seen only breakers with single interrupters doesn't mean there aren't other, different designs out there. Check out the following article from ABB describing their GIS up to 1100kV, with four (!) interrupters in series.

http://www05.abb.com/global/scot/scot245.nsf/veritydisplay/85111ec6e670beafc125759900570136/$file/ABB%20Review%202009-01_92-98_en.pdf

__________________
To get the right answers, first you need to ask the right questions.