Hi friends.
I have a 3 phase system .
My R-phase is carrying 100 Amp.
Y-phase is carrying 95 Amp.
B-phase is carrying 130 Amp.
what should my cable rating?
Friends plz tell the formula also.
Pathfinder Tags: cable sizing
Re: cable sizing
08/15/2011 11:45 AM
Your cable size should follow the appropriate building codes. This will follow the maximum current your service can provide, not the current you draw.
Good Answers: 44
Re: cable sizing
08/15/2011 11:45 AM
Cable rating is for maximum of the designed load, plus a percentage derived from the tables of your local design authority. You don't have different cable sizes for each phase, that's for sure.
Since you have the usage for each, I would continue with that and complete a full power quality survey for each panel and subpanel to figure out why you are imbalanced between phases. You have to take into account the sizing of the neutral and the rating of your transformers to make sure you design a healthy system. Since I see a 75% difference between your 2-3 you will want to check into that. You must also determine your reactance and PF for the system. There is so much to go into it is too much for this forum.
As far as the formulas go, you can google them or use your handbooks from your local authority.
Re: cable sizing
08/15/2011 12:13 PM
There is a table the gives cable ampacity located here. However, there are
code rules that may require you to use a different size. You need to get someone who is capable to assist you in this selection. Maybe an engineer.
Re: cable sizing
08/15/2011 12:21 PM
Hi.
your table is usefull . thanks
Re: Cable Sizing
08/16/2011 3:52 AM
Having trouble with British Standard 7671, eh?