How to Disable Field Supply of Lenze DC Drive 4903

08/16/2011 2:48 AM

I have a Lenze DC drive 4903 which gives 340VDC field out put. The application is a motor which field is rated for 110VDC. I have arranged a separate source for 110VDC for that motor's field supply. But now drive is halted as no field is connected with drive.

I tried to set ZERO the field current by parameter C083 (original value in this parameter was 3.6), putting "0" in this parameter make "Ready" the drive (during field disconnected) and functioning well but if we cycle the power then again "3.6" loaded in C083. I also reduced the value in C231 by 10% (min) but problem did not solve.

Please assist how to disable the field.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#1

Re: How to disable field supply of Lenze DC drive 4903

08/16/2011 3:25 AM

One most simplest way is to connect some dummy load like filament lamps to field supply.

__________________
Subramanyam
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: How to disable field supply of Lenze DC drive 4903

08/16/2011 4:54 AM

The drive is protecting the motor. It senses no field current so will not pass the armature current. As has been suggested you could apply a dummy load. But to be honest with you I think you are being foolish importing a separate field supply, if it fails the drive can't protect the motor.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#3

Re: How to Disable Field Supply of Lenze DC Drive 4903

08/16/2011 10:29 PM

Once you have changed parameter C083 you must save the parameter set for the next power up. Do this by placing 1 in parameter C003.

__________________
johny451
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#4
In reply to #3

Re: How to Disable Field Supply of Lenze DC Drive 4903

08/17/2011 12:36 AM

Thank you Mr. Johny. My problem solved by 100%.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#5
In reply to #4

Re: How to Disable Field Supply of Lenze DC Drive 4903

08/17/2011 12:46 AM

You are most welcome but do take note of TonyS's comments. Failure of the field supply will cause the armature to draw massive current. Can you tie the field supply into a drive disable somehow such that if the field supply is at least powered off the drive will not start?

__________________
johny451
Register to Reply
Active Contributor

Join Date: Jul 2011
Location: UK
Posts: 18
#6

Re: How to Disable Field Supply of Lenze DC Drive 4903

08/17/2011 6:34 AM

Field windings are rated in current not voltage. The voltage rating means it needs around 110V DC to achieve the nominal rated field current. There is however some times an insulation issue (see below) You normally just need to set the field current in the drive to the nameplate to run at base speed, when you measure the volts it will be around 110V DC (depending on how good your multimeter is at dealing with harmonics)

I have run lower voltage DC motor field's from higher voltage Alstom/Cegelec/GEC field converters quite happily and have occassionally had to put in transformers on the AC supply to field converter section when I was concerned about the rating of the insulation - however in these instances (a) you need a separate AC supply (separate from the armature convertor) to the field convertor and (b) the transformer needs to be around 5 times higher rated as there will be a significant high frequency component that would cause a nominally rated transformer to over heat.

In YOUR case I would suspect that running a 110V DC motor field from a 340V DC rate field convertor to be fine, the insulation is very likely to be fine at that lowish voltage.

This way you will get the drive protection

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#7
In reply to #6

Re: How to Disable Field Supply of Lenze DC Drive 4903

08/17/2011 7:12 PM

Good point machine builder. If the drive allows you set set a given field current what not just set the correct field current from the motor specs and run it off the drives field supply?

__________________
johny451
Register to Reply
Active Contributor

Join Date: Jul 2011
Location: UK
Posts: 18
#8
In reply to #6

Re: How to Disable Field Supply of Lenze DC Drive 4903

08/18/2011 3:33 AM

To be quite honest I should have said that if you are dealing with a variable field then any issue with the voltage will be from the level of the AC supply rather than the average DC voltage. The AC supply will be switched by the field convertor and there will be voltage spikes well in excess of the average DC voltage so if the supply is for example 480V AC and the field is nominally 110V DC you will see could voltage spikes up to 1.414 times the rms value of 480V ie 679V. This might be too high for the field winding especially if it is an old motor that expected to see a smoother DC supply.

Strictly you should check with the motor manufacturer that it is suitable.

Unfortunately it is hard to get such data on older motors. The normal course is either just to try it but be prepared for a failure or if you really are too concerned to add the transformer as suggested earlier

Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#9
In reply to #8

Re: How to Disable Field Supply of Lenze DC Drive 4903

08/18/2011 5:16 AM

Thanks to all for participating in this discussion.

Yes I do have protection system if external field supply has some problem, drive would be shut down.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Johny451 (3); kvsubramanyam (1); machine builder (2); Signode (2); TonyS (1)

Previous in Forum: Fault Current Measuring in CT's   Next in Forum: What is Traffic Signal Termination Pillar?

Advertisement