Fault Current Measuring in CT's

08/16/2011 2:11 AM

- 11/0.415 kV Power transformer capacity: 2500 kVA (given);

- Transformer % impedance (Z): 6% (assumed);

I = kVA/ (0.415x1.732) = 2500/(0.415x1.732) = 3478.11 A, CT with primary current of 4000 A to be selected.

Calculation of max. Fault Current

Ift = kVA/ (0.415x1.732x Z)

Ift = 2500/ (0.415x1.732x0.06) = 57968.59 A (rounded to 58000 A)....

my question is how can the CT measures the fault current which is more than the rating of the current trans 4000/5....????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: fault current measuring in CT's

08/16/2011 3:49 AM

It won't. The circuit protective device(s) will operate before the CT reading will be noticed, disconnecting the circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: fault current measuring in CT's

08/16/2011 5:53 AM

Have you ever wondered how protective relays sense and act on short-circuits ? After all, the relay is the 'brain' of the circuit breaker.

This subject of CTs, Rogowski sensors, and Hall-effect sensors is too big to cover here. You need to study some documents available on the internet.. here is one good site : http://www.kappaelectricals.com/technical.html

Another good document is ect170.pdf by Schneider Electric

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Fault Current Measuring in CT's

08/16/2011 10:17 AM

You need a detailed course on current transformers, I fear! Depending upon the class of the CT and the Instrument Safety Factor (ISF) or the Accuracy Limiting Factor (ALF), a CT remians accurate up to a certain multiple of its rated primary current and after this limit, the CT saturates.

I suggest you attend to our training programme on Protective relaying.

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#4

Re: Fault Current Measuring in CT's

08/16/2011 12:23 PM

It is not the CT that measures current. CT simply transforms high current to low current based on turns ratio, saturation effect etc.

The secondary current is used for measurement or protection.

The fault current can exist as long as the fault exists. This may be few cycles to few seconds depending on the type of protection and fault clearance provided.

Numerical Digital relays, record shortest possible duration fault current within few cycles. They work collecting samples of AC waves with an AC cycle, estimating the fundamental , harmonic components through fourier transforms, comparing the values to set values and triggering the protective mechanism if needed.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Active Contributor

Join Date: Jul 2011
Posts: 13
#5

Re: Fault Current Measuring in CT's

08/17/2011 4:30 PM

Hi Mohsinhamid

I see that the guys are giving you a lot of fancy answers on your question asked...I think they do confise you a lot....

You must just re-calculate your fault current ...it is far to high...you can not get fault current from a 2.5MVA transformer of that magnatude that you calculated...you must get the correct formula for the calculation....

To come back to your question:

If you get a CT 4000/5 then it is the nominal current where it can operate continuesly

On a CT name plate you find: STC=40kA/3s (Short time current)

That means that your CT can withstand 40000Amp for 3 seconds....then you must select suitable protection relays to clear the fault asap

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Fault Current Measuring in CT's

08/17/2011 7:42 PM

I think, if others have given fancy answers, you have given an erratic answer and an unfair comment on others' answers.

And the OP is not wrong in calculating the fault current from a 2.5MVA Transformer to be 58kA. So, to say, it will be very close to that value.

I"k for a three-phase fault at the outgoing terminals of a transformer is given by:

I"k = Trf. FLC on the 433V side / % impedance of the Trf.

And, going by IS 2026, the typical impedance for a 2.5 MVA Trf. is: 6.25%.

FLC of Trf. is : (2500 x 1000) / (1.732 x 433) = 3333.52A;

I"k = 3333.52 / 0.0625 = 53.34kA.

And assuming that the short circuit happens after the location of the CT, the CT will still have to carry this current for the co-ordinated fault clearing time.

And, going by IS 2705, the duration of STC for CTs is not 3 sec. but 1 sec. For, 3 sec. STC duration would increase the cost & size of the CT.

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#7
In reply to #6

Re: Fault Current Measuring in CT's

08/17/2011 9:44 PM

What is the source impedance considered?

Source impedance cannot be zero and it will reduce the fault current.

Apart from the source impedance, pre-fault load flow conditions and thevenin's voltage also influence actual fault current.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Active Contributor

Join Date: Jul 2011
Posts: 13
#10
In reply to #6

Re: Fault Current Measuring in CT's

08/25/2011 4:50 PM

Hi EE65

You are correct in saying the CT STC duration is for 1sec...I got confused with something else that is for a duration of 3sec...we work a lot with CT's and it is actually on the name plate

Register to Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#8
In reply to #5

Re: Fault Current Measuring in CT's

08/19/2011 5:55 AM

To make life simpler there is a nice little App called Transcalc, it's available on both Apple & Android, it calculates FLC and 3 Phase Short based on transformer ratings

Register to Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Fault Current Measuring in CT's

08/19/2011 6:39 AM

Good one. First good reason for me to own an android phone ! GA ...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers: