Transformer Impedance for the VSD

08/18/2011 5:53 AM

I have to supply three winding transformer to supply a 12-pulse VSD.

Later from the VSD Manual, I found out about Minimum Leakage Reactance for the transformer. After I calculate the transformer impedance voltage, I got the value of 8.7%, while I already ordered transformer with impedance of 6%.

What would be the effect of the transformer's impedance to the drive? I'm sure it's not about the kA rating.

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#1

Re: Transformer Impedance for the VSD

08/18/2011 5:59 AM

The transformer is designed to supply two three phase bridge rectifiers with the three phase applied to one rectifier phase shifted relative to the other.

The value of the impedance is usually not critical except for affecting the voltage regulation.

The important point, is the impedance of the transformer as it is seen by each bridge rectifier.

Both impedances must be equal or there will be an imbalance in the current between the two rectifiers and the harmonic cancellation will be reduced. You could also cause the failure of one of the bridge rectifiers if the curent imbalance is too bad.

Best regards,

Mark Empson

http://www.power-harmonics.co.nz

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2

Re: Transformer Impedance for the VSD

08/18/2011 6:41 AM

I think, You asked for the leakage reactance, causing the eddy currents & consequently, voltage distortions. This is understood to be to control the harmoics i.e. practially, 5th harmonics causing neusance firing of the thyristors.

If similar problem encounters with the ordered transformer, you may put filter

solve the problem.

__________________
Exploring the Science of Electricity
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#3
In reply to #2

Re: Transformer Impedance for the VSD

08/19/2011 3:06 AM

@ harry potter

It's a 12 pulse rectifier, that means the 5th harmonic is quite low.

What I understand is: the lower the impedance of the source, the 'rigid' the source will be, as there will be only small distortion at the voltage of the source.

But in the catalog of siemens drive, it mentions about Minimum leakage reactance for the transformer. It means it would be better to have higher impedance.

Could somebody please help me with this issue?

Thanks

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4
In reply to #3

Re: Transformer Impedance for the VSD

08/20/2011 5:50 PM

Higher leakage impedance smooth out the current and reduce the ITHD at the expense of VTHD. If nothing else is feed from the transformer secondaries, the VTHD is not an issue (usually) for the drive.

With high leakage inductance, the rectifiers current will be less "spiky" than when using a hard supply.

You could add supplementary line chokes between the transformer and the drive to get the desired inductance.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments