Recently I have face the following motor over load issue at my work place :-
Project head over the new process equipment to operation, I receive a complain that the equipment away over load trip after few hours of operation.
- I have check the motor resistance and insulation , motor connection and tightening check , no fault was found. Uncouple the motor and rotate the pump and motor and solo run the motor all are normal and our grip supply voltage is 433 Vac.
- Run the motor with load the full load current is 26.5 Amp and is lower them the motor rated current.
- Check the motor detail below :
Motor rated 400Vac, 11KW. 28 Amp, 0.6 PF.
GE motor manager 501 set at 433 Vac , 11KW, FLC - 28Amp
Over load setting is 105 %
For 433Vac(Supply Voltage )
FLC = 11x1000/1.732 x 433 x 0.6
= 26 Amp.
For 400Vac(Supply Voltage )
FLC = 11x1000/1.732 x 400 x 0.6
= 28 Amp
1.What is the correct setting need to input (26Amp or 28 Amp ) to the GE multi links motor manager 501 controller, If is the wrong setting cause the motor over load ?
2. Any impact when the motor require to operate at 24-7/365 days ?
Thanks & Regards
Chan kum Kong