Max Allowed ZS for Schneider mccbs

08/18/2011 11:21 AM

can anyone tell me where i can find max zs values allowed for schneider type mccbs ranging from 32amp to 800amp . thanking you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: max allowed zs for schneider mccbs

08/18/2011 2:05 PM

zs? Do you mean Zero Sequence current? Do your MCCBs have ZS protection built-in, as in having external core balanced Zero Sequence Current Transformers (ZSCT)? If not, ZS is a non-issue, a strandard MCCB will not be capable of detecting nor reacting to a Zero Sequence current siutation directly. Even if you were referring to solid state MCCB trip units, they will typically have Residual Current detection for ground (earth) fault detection, ZS is an option because it requires that external ZSCT.

Assuming that's what you mean by "zs".

PS: We can't read your mind and acronyms have lots of different meanings, even in the same context.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Max Allowed ZS for Schneider mccbs

08/19/2011 5:49 AM

Maximum values for Zs are in BS7671-2008. They aren't manufacturer specific. Or contact the manufacturer.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Max Allowed ZS for Schneider mccbs

08/20/2011 1:35 PM

So Tony, what is Zs in this instance? Source impedance?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#4

Re: Max Allowed ZS for Schneider mccbs

08/21/2011 1:18 AM

zs-> earth fault loop impedance

http://pws.schneider-electric.co.uk/internet/pws/literature.nsf/luAllByID/NKIY-5JUHSL/$file/MGD5032_section2.PDF/

page-6........................

Zs= Uo/Ia

Where

Zs = Maximum earth fault loop impedance.

Uo = Nominal phase voltage.

Ia = Current ensuring automatic operation of the protective device.

Ia for circuit breakers is the mean tripping current as follows:

Type B = 4 (typical)1 x rated current

Type C = 7.5 (typical) x rated current

Type D = 12.5 (typical) x rated current

Ia for fuses are appropriate mean values from AS 60269.1

__________________
shamith gambhir, electrical engineer
Register to Reply