33 KV Line

08/19/2011 12:13 PM

Hello friends, We have an independent 33 KV Feeder about 22 Km long. Recently it tripped on phase to phase over current and yellow phase to earth fault, as reported by the substation operator at the sending end. At our end there was no fault indication. The line was checked for IR value. For the entire length the phase to phase IR was 20 M ohm and pass to earth it was 6 M ohm in all the phases. IR was checked with a 5 KV hand operated Meggar. But the line could not be charged as it again tripped on earth fault. Is there another way to test a 33 KV line. Regards.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: 33 KV Line

08/20/2011 11:10 AM

Use the correct test set. 5 KV test on a 33KV line and you get low results.

Get some one in that knows what they're doing, you don't!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: May 2011
Posts: 4
#3
In reply to #1

Re: 33 KV Line

08/20/2011 11:40 PM

Tony S, I sense dark Sarcasm in your post and I also feel you frothing in the mouth!

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: 33 KV Line

08/21/2011 5:36 AM

The only thing that is frothing around me is my glass of beer.

Be honest do you expect to get meaningful readings from a 5KV Megger?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: May 2011
Posts: 4
#5
In reply to #4

Re: 33 KV Line

08/21/2011 6:30 AM

Guru Ji, Please let me know what to use. I am being honest am looking for advise. No offence was intended. Regards

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: 33 KV Line

08/22/2011 9:14 AM

Do you have access to 56 / 36KV DC test equipment for line - line / line - earth testing. If not it's cheaper and safer to get a specialist company in to do the testing.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7
In reply to #6

Re: 33 KV Line

08/22/2011 12:33 PM

Kssoin, TonyS is correct - your next step is to test with equipment that provides a voltage at approximately the operating voltage of your line. The likely culprit is a surge arrester or insulator that has a defect or damage of some sort. It is capable of sustaining the 5kV DC of your megger, but when the voltage is raised to operating leve, it flashes over and trips.

The original cause may have been something that shorted phase-to-phase and to ground, and damaged the insulator or arrester. You didn't say if this is an overhead line. Do you have large birds that tend to roost on poles, or large varmints (raccoons, etc.) that could climb a pole? Have you done a close visual inspection using binoculars to see if you notice any burn marks, or a dead animal around the base of a pole?

If it is underground, then you need to check any places where the line surfaces (padmount switches or transformers, pole risers, etc.). Also, if you have a relatively higher impedance fault than can show on your megger, you may need to use a cable thumper/burner to force the short to low-impedance and to help locate it.

You will need to get a professional testing company in to look at your problem if you aren't able to do any of these.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#9
In reply to #7

Re: 33 KV Line

08/24/2011 10:59 PM

Peter T is dam right in his recommendation. I was maintaining a similar 22 KM 33 kV OH line which was our own distribution system. Similar earth fault occurred due to cracked insulators which could not be found on normal megger test. I used to apply a HV puncturing and there after I could locate the faulty insulator by line petrolling. The lightening protector after a discharge after heavy lightening will show similar results and can be confirmed after disconnecting them and switching on the line. Under faulty conditions the lines should not be charged repeatedly as it can damage the breaker itself.

Since our line was passing through forest area often monkey fault and snake fault occur at times ( both of them are instantaneous earth fault which re occur ). So line petrolling is essential to locate such earth faults. In case of UG cable the end termination is another such culprit where the Megger test fails.

Register to Reply
Anonymous Poster #1
#2

Re: 33 KV Line

08/20/2011 7:26 PM

Notice that 22km is also a multiple of 11; no doubt this induces some kind of resonant feedback that could amplify voltage (and thence current) enough to trip protective devices.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jul 2011
Posts: 13
#8

Re: 33 KV Line

08/24/2011 5:06 PM

We have a 80Kv Pressure test set in the store...you are welcome to use it to locate the fault

Phase to phase fault may be clashing conductors

Phase to earth fault may be pin insulators that needs to be changed...could also be a tree in the line...or birds making their nest on the structure....

They guys must drive and inspect the line

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Kssoin (2); MJ Jordaan (1); PeterT (1); TonyS (3); V.I.Abraham (1)

Previous in Forum: About Ratio of Sodium Bicarbonate in Water for LRS   Next in Forum: Leakage Current And Voltage

Advertisement