Cable Voltage Drop Calculation

08/23/2011 2:23 AM

dear all,

we are planning to construct a long conveyor from mines to plant.the distance is approximately 35KM.for material conveying 5 no's 11KV motor shall be used for different distances.my question is. in that 11KV cable is more economical or 11 KV overhead system.

next is if we are using 11 KV cable what about the volatge drop. i have calculated the volatge drop.but the thing is first motor i have calcualted the motor volatge drop. then how shall i find out the second motor voltage drop.because all the 5 motors are connected in loop in & loop out arrangement.all the motors shall run one by one.so starting volage drop is not on issue.so kindly help me in this regard.

regards,

N.Ganesan

__________________
Knowledge Sharing
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable volatge drop calculation

08/23/2011 5:01 AM

11kV is not the sort of stuff for the untrained to play about with. So, hire a competent Electrical Engineer to solve the problems.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Cable volatge drop calculation

08/23/2011 6:03 AM

Your going to start a 35KM conveyor in one start, all be it with 5 motors?

I wish you luck!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator
India - Member - New Member

Join Date: Jun 2008
Location: Tamilnadu,india
Posts: 64
#3
In reply to #2

Re: Cable volatge drop calculation

08/23/2011 6:09 AM

it will be with 5 motors

__________________
Knowledge Sharing
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Cable volatge drop calculation

08/23/2011 8:24 AM

It might be easier to build a railway between the places.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #3

Re: Cable volatge drop calculation

08/23/2011 2:03 PM

You're seriously going to start 5 motors driving a 35KM conveyor?

You need your bumps feeling.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: Cable Voltage Drop Calculation

08/23/2011 3:33 PM

How are the motors being controlled? It sounds like you are wiring them so they can start in sequence one after the other, with the motor speed being slowly increased to prevent catastrophic equipment failure.

Can you provide more information please.

__________________
jack of all trades
Register to Reply
Commentator
India - Member - New Member

Join Date: Jun 2008
Location: Tamilnadu,india
Posts: 64
#9
In reply to #6

Re: Cable Voltage Drop Calculation

08/24/2011 12:26 AM

thanks for your information.

the thing is our project team is proposed conveyor(type of conveyor not mentioned.) for through out the length.so they are asking electrical team for techno commercial feasiblity.

still we are searching the details in this regard. for example we are putting 3 feeders for every conveyor motor like incomer feeder(getting power from previous feeder),motor feeder(supply to motor),outgoing feeder( loop in-loop out).if motor is fixed speed in this option is ok. for variable speed application we have to consider 690V converter duty motor,690V drive & 11/690V converter duty transformer(with OLTC=+/- 10%).for controlling the motor start we shall go with any wireless or radio frequency.Kindly send your suggestion.

__________________
Knowledge Sharing
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #9

Re: Cable Voltage Drop Calculation

08/24/2011 3:27 PM

It sounds like you just need to consider the 5 loads (voltage drops) connected in a series arrangement and size the cables for the expected starting and operating currents accordingly.

If you are using a ring main system (which is still a little unclear) with the possibility of powering the conveyor motors from either one end or the other then you would need to size the cabling for being powered from either direction (in which case the cable size would be large at both ends and may reduce in the middle).

__________________
jack of all trades
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Cable Voltage Drop Calculation

08/23/2011 4:44 PM

In my world 35 km = 21 miles. That does not seem reasonable. Has it been done before? Utilities find that the overhead line will be cheaper to build. What size motors? I assume the motors will be equally spaced along the 21 miles.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#8

Re: Cable Voltage Drop Calculation

08/23/2011 9:54 PM

your question is not clear enough...a rule of thumb we practice here is having your cable sized up at higher voltage with respect to the operating voltage..this is to compensate for in rush currents, voltage drops, and etc..you say your motor is operating at 11kV system, if i were to size up your cable i would go for 15kV rated cables at same operating current level with your 11kV one...

if you're worried enough with your voltage drops, how about stepping up your voltage to a much higher level...

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ganeshakce-electrical (2); jack of all trades (2); PWSlack (2); rockraiden (1); TonyS (2); wareagle (1)