PLC5 Trouble

08/30/2011 2:28 PM

I've gotta interesting problem. I have a motor o/l fault showing on a hmi screen when there is no fault. I've check the wiring going to the mcc can back to the plc and find no problems. The starter is not tripped out, the coil for said starter is good I changed it out for giggles and im monitoring the old coil on a new starter. Anyway the starter gets its run command via ethernet and if there was a problem there it would come up as a comma fault between the plc and the hmi. So I ask you could I be losing the input on the card momentarily. Due to a bad port on the card. Oh and the aux in the starter are good also. Than you for ur time

__________________
MattJohnson
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: PLC5 Trouble

08/30/2011 4:32 PM

No way to know without knowing your wiring and programming. But I would not waste a lot of time with coils, contactor aux contacts and things like that. TYPICALLY if you have a hardwired interface, you would have the N.O. aux contact of the OVERLOAD relay wired to a PLC input. If that contact is welded closed, that would explain it. But also if the wires for that circuit are improperly run and are picking up an induced voltage, that may be triggerring your input too. Could be a lot of other things too.

I would start by identifying the PLC input that is associated with determining that the motor starter detects an overload. Lift the wire off AT the PLC input and make sure the input status changes. If it doesn't, then it's likely a bad card or something else in the PLC. If the status changes when you lift the wire, the problem is in the circuit. Put it back on and lift the wire AT the overload relay. If the status changes, its the relay. If it doesn't, then you are getting voltage onto the input wire from somewhere else.

If there is no wire coming from the OLR N.O. aux contact, then your PLC programming is using some other method of detecting an OL condition. Sometimes (bad idea), a programmer will use logic such as "If a Start command was given AND no feedback was received, THEN it must mean it is tripped on Overload". It's not a good logic plan, but some people are cheap and don't want to have the OL aux. contact wired back to the PLC, I see it all the time. the problem is, it is not truly indicative of an actual overload trip, could be a LOT of other issues.

Good luck.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: PLC5 Trouble

08/31/2011 4:10 AM

GA, but the system is plugged right now and not accepting votes.

BTW, congratulations on crossing the 300 mark, and thanks for many informative postings!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: PLC5 Trouble

08/31/2011 12:32 PM

Awww shucks, hadn't noticed. Thanks.

<shuffles feet>

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Aug 2010
Location: alabama
Posts: 81
#4

Re: PLC5 Trouble

08/31/2011 9:06 PM

Sorry for not getting back until now. We'll it was the remote I/o card on the main rs5000 rack. I do believe we gotter wooped. Thanks for the help

__________________
MattJohnson
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#5
In reply to #4

Re: PLC5 Trouble

09/02/2011 12:12 AM

1) What is the rating of input card, 24VDC or 110VAC?

2) Are the motor starter and remote I/O card wired in same cabinet?

3) What is the normal state of aux contact of overload, normally CLOSED (input remains ON).

Such kind of "momentarily" problems take time to resolve.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Commentator

Join Date: Aug 2010
Location: alabama
Posts: 81
#6

Re: PLC5 Trouble

09/02/2011 8:43 AM

Its just a card that's a little old 3 or 4the yrs old. We got a new one and so far we've had no problems

__________________
MattJohnson