Please Help Design a Dummy 230v ac Electrical Load.

09/03/2011 6:35 AM

Hi

I'd appreciate any help you can give me on this as although I'm an approved electrician, I'm not an expert on electronics so here's hoping.

My job is to perform the periodic inspection and testing of electrical installations in line with BS7671. Sometimes I have to trace unknown circuits and I do this by plugging in something like a toaster or kettle to induce a load on to the circuit, then would use a clamp meter to locate the load in the distribution boad. As utilising a kettle or toaster in this way isn't practical, i'd like help designing something which would probably resemble a 13 amp plug top on a flex with the flex running into a small plastic adaptable box. Inside the box (this is where you come in) ...... what would i need to replicate a load, maybe 10 amps so easily identifiable at the board. ie, transformer? resistors?

Thanks for taking the time out toread this post and I appreciate any help there might be.

Ian

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#1

Re: Please help design a dummy 230v ac electrical load.

09/03/2011 6:52 AM

Even if you can make this artificial load, it will not be a small plastic box, or more convenient than a toaster . 10 A at 230V is 2.3 kW, that is a lot of power to dissipate.

No matter what circuit you come up with , you have to dissipate this power away which ill require big fan and hugh heatsink, certainly not cheaper than a toaster

So, the cheapest and most practical way , though not elegant is still toaster, kettle or electrical stove.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Please help design a dummy 230v ac electrical load.

09/03/2011 8:44 AM

Stick with the kettle, you can have cup of tea to celebrate finding the cable.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
4
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3

Re: Please help design a dummy 230v ac electrical load.

09/03/2011 9:54 AM

If it was me and I had to do routine load testing such as this I would design a load bank unit into a metal tool box.

Basically it would be a heating element in a duct that has a fan blowing air through it to keep it cool all mounted inside a converted over tool box of some sort.

If necessary as a added assistance in finding the load you could put a simple timer circuit that blinks the load on and off every few seconds so you can distinguish that from any other similar sized loads that may be present. With the blinking load you don't need much current draw to find it that way as well!

Register to Reply Good Answer (Score 4)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#6
In reply to #3

Re: Please help design a dummy 230v ac electrical load.

09/03/2011 11:48 PM

A 1500 watt portable heater (120v 12.5a) is exactly what you are describing and it is inexpensive and readily available. It already has a plug on it also. If needed an adapter cord of 14-3 or 12-3 wire with an appropriate socket on one end and well insulated clamps on the other end will facilitate testing other than circuits with outlets on it.

I have used this for many years when I need a dummy load within this working range. It also doubles as a heater during the winter if needed.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12
In reply to #3

Re: Please help design a dummy 230v ac electrical load.

09/04/2011 1:09 PM

do you really do it that way in the USA? You would not be allowed on site with that in the UK.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#4

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/03/2011 9:09 PM

Interesting.

After noticing that my generator wasn't quite working 100% during a recent power outage, I performed some maintenance and adjustment to it today. When I was finished, I wanted to load test it. I thought of the heaviest portable loads I could find, but none was as easy to grab and plug in as a toaster. Funny that you should ask about a load on the same day that I happened to use such a load.

The toaster is great for a quick and dirty test. But I have to agree with tcmtech. Mount a heating element in a metal tool box. Keep in mind that a heavy load puts out a lot of heat. Make sure not to leave it on in an enclosed area or near combustibles.

Lastly, load testing is one thing, but if all you need to do is trace a circuit, there are instruments that do just that.

Register to Reply
4
Member

Join Date: Jul 2008
Location: Bayport, Long Island, NY
Posts: 9
Good Answers: 2
#5

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/03/2011 10:53 PM

Why are you wasting your time with a toaster oven or load bank? Purchase a circuit tracer. It works by attaching a transmitter which sends a pulse through the circuit and can be identiifed by the receiver. Anywhere along the circuit.

I have been using an Amprobe circuit tracer for over thirty five years and it is a reliable cost effective tool.

__________________
True leaders are like Eagles, they do not flock. You find them one at a time.
Register to Reply Good Answer (Score 4)
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#10
In reply to #5

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/04/2011 12:59 PM

That's what I do, but I'm lazy. Takes about a minute, works great, costs less than $50 new, lasts a long time. A GA.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#11
In reply to #5

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/04/2011 1:06 PM

missed this first time around.. good answer from me. In fact its the ONLY answer required.

__________________
The square root of nothing is what you make it!
Register to Reply
Active Contributor

Join Date: Apr 2011
Posts: 12
Good Answers: 1
#7

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/04/2011 12:48 AM

Simple! What you want is a resistor, but a resistor requires a mineral oil bath to dissipate the heat, or, you need a blower to dissipate the heat directly to the air, so...wire a couple of high-power hair driers used by the ladies in series. The high power ones ought to draw 10 amps, and if they are the travel sized ones, you can reduce their footprint on the platform you choose to mount them on. Just remember - and this is important!!! Don't EVER use this in an environment where you may have combustible fumes. This is the same precaution you would take if you were thinking of using a propane torch or propane soldering iron. There is a possibility that the heating element could ignite dust drawn in from the fans, and ignite the fumes. Otherwise, Ohmite makes mil-spec resistors with anodized aluminum heat sinks built in to dissipate the heat, and the ones in the range you're talking about are about the size of a pound cake. Even these are made to mount to something to dissipate most of the heat. In the TV and elevator industries, transmitters and motor control circuits would routinely have huge resistors like this to dissipate energy, but then again, forced-air cooling.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/04/2011 3:10 AM

since when has a PI required you to do what you've suggested with a dummy load. If you think about it any item of equipment that draws a current is NOT a dummy load.

I strongly suggest to get back to your book and 2391 guide book and study again.

do you have your C&G 2391 certs?

CR4 members.. if you don't know anything about BS7671 C&G 2391.. then please DO NOT offer answers to this post.

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Sep 2011
Posts: 2
#13
In reply to #8

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/05/2011 3:01 AM

I'm not sure you understood what I was trying to achieve or maybe It was me not going into enough detail......

I have had my C&G 2391 and 2400 amongst a few othes too, for quite some time now. My problem is I work for the MOD and the 726 buildings I look after vary in age from grade 1 listed over 250 years old to modern day. some of the wiring has not been upgraded since installation and hardly any is marked with its designated circuit indentification. Some of these buildings contain secret and top secret equipment and computer servers etc and because of this there is no way it can be switched off. There are usualy a number of distribution boards all in the same vacinity (again, not marked with what they are supplying). As I said, I am unable to turn them off to trace them and as for a circuit tracer, they may be ok in certain situations, (i've had one for years) they are completely unreliable in this situation. That's why i went down the route of introducing a load to the circuit of a known value so making it easy to trace at the distribution board.......

Being pretentious is easy when you're ignorant of the facts so next time maybe just ask?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#14
In reply to #13

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/05/2011 12:10 PM

If the facts aren't provided how can anyone be accused of being pretentious?

And if you think I believe that computer servers are fed off random unidentified distribution boards, your dreaming. For such "high security" establishments do you think for one minute you would be allowed to take some home made device in?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#15
In reply to #13

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/05/2011 1:47 PM

Thank you Tony....

Ian, my dear boy..... I've been called lots of things in my long and fruitful career.. pretentious is not one of them.. however something new to add to the list.

As Tony aptly put it... a lack of info does call for a certain amount of scepticism... and now you have admitted you work for the MOD and have told the WHOLE world what you do, are you now looking for a new job?

Have you EVER heard of the old saying "loose lips sinks ships" ?????

I'm sure that the MOD HQ in Bristol would love to know that you are passing freely on a open medium your job description and job content.

When I was in the Army.. people who had said less were hauled away by SIB, never to been seen again.

If I was you, and before I do, you contact your chief of Security, show him what you've put, and get CR4 admin to delete you your post and your enrolment, as you have now painted a target on your back.

your IP address is easy to track... and SB just love this kind of thing

You silly silly boy!

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#17
In reply to #15

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/08/2011 2:55 PM

If this facility is so important then this type of work needs to be contracted out to someone who can do it correctly and on-time.

If not, then someone needs to get some schooling. Make your boss pay for it if they want to pass their inspections.

Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#16
In reply to #13

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/05/2011 4:25 PM

Another potential solution for you:

Many years ago an electrician who was working for a contractor on a project I was in charge of loaned me a signal tracer that is identical to those used by comm personnel and telephone personnel for tracing of communication wiring. Put the signal generator (a very small box with two leads) on one end of the circuit (either hot-neutral, hot-ground or hot-hot) on one end of the wires under test and use the sensor unit to trace down the other parts of the circuit. Sensor does not have to touch the live circuit, just be in close vicinity to the wire. Worked every time it was used with no fuss, no risk and always accurate. Only problems occurred when it needed fresh batteries for receiver.

The best part was that the unit could be used on either dead or live circuits up to 600V, not just comm wiring. It had been dropped so many times that it was held together with electricians tape. When I went to return it to the electrician he refused to take it and gave it to me as a thanks for working on the project.

I would suggest you look into something like this. Perhaps FLUKE or some other manufacturer of instruments. Don't think it would cost more than $60-100 US for sender and receiver.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#9

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/04/2011 7:35 AM

you cannot be serious

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#18

Re: Please Help Design a Dummy 230v ac Electrical Load.

09/08/2011 2:57 PM

For a quick and safe temporary load bank you may want to use a bank of halogen lamps. It's quick and easy and gives reliable results through the use of switch-in circuits for additional bulbs/load.

Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: