Voltage Leakage

09/06/2011 3:14 PM

May I ask some help from fellow electrical practicioners. Recently we have an upgrade project with our Water Treatment plant using PLC and HMI (HumanMachine Interface). What we did is we include some indicators not related to Water Treatment Plant like indication of Standby generator status like "Run" "Fault" & "Ready". Those indications were display in LCD Monitor thru PLC. The input to PLC came from external relay which will be turn "on" by Generator local relays. We used a shielded cable with the following specifications:15 cores x 2.5 sq. mm, 500 volts shielded, pvc/pvc, 30 degree c. the supply voltage of the relaycoil is 220 VAC, 60 Hz coming from control transformer located at the PLC control Panel. the distance between Generator panel & PLC panel is about 50 meters. Now my problem is; their is a leakage voltage ranging from 80 volts to 120 volts among wires in the cables when suppose to be only 1 wires is live and the other should have no power unless the intended relay in generator is energized and close the contacts. we already megger the insulation between wires and it is all infinity. the cable is lay in the wall thru PVC pipe and about 10 meters is layed in cable trays and mixed with other cables having voltage of 380 volts for motors supplies. May you help the probable cause of this leakage which result a ruttling of our relays that give input to PLC.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Voltage Leakage

09/06/2011 5:31 PM

It's difficult to understand what you mean by "leakage".

If you're measuring this voltage on conductors which are not terminated - i.e. not connected to anything - and you're measuring with a high impedance voltmeter (e.g. a DVM) , you will inevitably measure large AC voltages - picked up by inductive and/or capacitative coupling.

If these conductors are not used, connect them to earth/ground at one end. If your measured voltage still doesn't disappear, try measuring it with an old-fashioned AVO, or put a 1K resistor across the test leads.

N.B. If the resistor is really seeing 120V, it will be trying to dissipate about 14W, so (unless it's a big'un) it will give up the smoke (which is its electrical life) and die.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #1

Re: Voltage Leakage

09/07/2011 8:39 AM

<...put a 1K resistor across the test leads...>

Or a filament lamp.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#9
In reply to #8

Re: Voltage Leakage

09/07/2011 9:16 AM
__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Off Topic (Score 5)
Anonymous Poster #1
#12
In reply to #1

Re: Voltage Leakage

09/07/2011 1:21 PM

we measured both conductors terminated and not terminated. those already terminated, we disconnected it and taped the other end and measure the voltage between conductor and neutral (earth). the neutral wire s is not part of the 15 cores cable. we already did like what you suggested to earth the spare conductors when we first encounter the problem. it reduced the voltage reading by 40 - 50% only and the relay still rattle if we connect to coil any wire and the neutral wire if one of the wire is connected to the supply source which is 380/220 control transformer. btw thanks for the knowledge you shared.

Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#14
In reply to #12

Re: Voltage Leakage

09/07/2011 6:21 PM

This is an "I'm Desperate - Get Me Out Of It" solution. With a connection to a relay coil which is rattling, put a resistor in parallel with the coil. Make it about half the resistance of the coil (which you can measure with a meter) and make sure it can take a bit of power without going puff. 1W should do it - but do some sums to check (or make it 4X the VA rating of the relay coil to be sure).

The proper solution is to use suitable wiring (individually shielded twisted pairs, with the screens grounded at one end only).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#17
In reply to #14

Re: Voltage Leakage

09/08/2011 3:28 AM

N.B. You could use a filament lamp instead of the resistor!

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2

Re: Voltage Leakage

09/06/2011 9:16 PM

Check for all terminal connections.Is it as per the circuit?

Reply
Associate

Join Date: Dec 2009
Location: Kota Kinabalu, Malaysia
Posts: 39
#3

Re: Voltage Leakage

09/06/2011 9:36 PM

These voltage 120vac you measure from which terminal, do you measure from live to ground?

Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#4

Re: Voltage Leakage

09/06/2011 11:23 PM

You should go back to school and learn a bit about electrical stuff . . .

Voltage does NOT leak . . . it is current that does the 'leaking' and voltage is the 'indicator' of the problem.

Your problem is caused by having power and signal wires running in the same cable. The "shielding" you are talking about is likely on the outside of the cable - YES? This does not do anyone any good . . . .

You need a cable wherein EACH PAIR OF WIRES will be shielded separately . . . to separate the AC power circuits from the signal circuits.

Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#5
In reply to #4

Re: Voltage Leakage

09/07/2011 12:00 AM

voltage is not the indicator . . . . voltage is the cause . . . when the isolation is breached (broken) then the resistance offered is lowered and the voltage is able to overcome the resistance to establish the current . . . the current is the effect . . .

also - current in one conductor can create a magnetic field in the neighboring region leading to an induced emf (voltage) across other conducting elements . . . resulting in currents being established in those conductors if a closed path is available . . . . in such a case no breakdown of isolation or reduction in resistance of the insulator may be in evidence . . .

Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#6

Re: Voltage Leakage

09/07/2011 4:55 AM

I would suggest that you change the system to 24VDC over the cable to elimate impedance caused over this 50m cable.

Joe

Reply
Anonymous Poster #1
#11
In reply to #6

Re: Voltage Leakage

09/07/2011 1:13 PM

yup we did it already and its working well. I only want to know the cause of leakage.

thanks a lot for advised.

Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#13
In reply to #11

Re: Voltage Leakage

09/07/2011 3:28 PM

Perhaps you missed the point about the digital volt meter. Your standard electronic volt meter has a very high input impedance. This makes it sensitive to the slightest inductive link which you are calling leakage. Long parallel wires link magnetically the same way as they do in a transformer. This is why you should separate power feeds from control lines. The longer the run of wire, the better the linkage.

Realistically you can not transfer much power this way as it is very inefficient. But you will detect the presence of a voltage with certain meters. An analog meter may help but it really depends on linkage to power lines.

If you live near overhead power lines that run parallel to a nearby fence, you will be able to detect a voltage drop along the run of the fence.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#7

Re: Voltage Leakage

09/07/2011 8:23 AM

You are using shielded cable. Although this signaling cable should be separate from the power cables, properly installed shielded cable should eliminate induction from power cables. There are two likely causes:

1. Does the cable have one common shield around all the cores? If so, the one live wire is probably inducing voltage into the others. Shielding does not help if the the source field and the affected conductor are both inside of the shield. The ideal cable for this installation is twisted shielded pair. Each signal supply and return pair is shielded separately, protecting it from the others.

2. Is the shield connected to earth at only one end? If the shield is not connected to earth it is useless. If it is connected at both ends it can actually make things worse. Voltage induced into the shield causes a current to flow through a loop consisting of the shield and earth. That circulating current is right next to the conductors and will induce voltage into them.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#10

Re: Voltage Leakage

09/07/2011 12:25 PM

Use a 24 volt system instead of the 220 VAC control relay system. See to it that all shielded wires, the shields are terminated to ground /earth. Then run all signal wires through or contained in a separate metallic conduit (do not use PVC) which should also be grounded. Be sure all ground wires / shielded wires share the same ground plane.

__________________
vsar
Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#15

Re: Voltage Leakage

09/08/2011 1:07 AM

cable shield is used to protect interference cost by EMC.

take note not only inductance is present in the circuit we do still have CAPACITANCE.

The voltage that you have measured is caused by cable capacitance due to a long distance. We have line to ground capacitance and line to line or cable to cable capacitance. Theoretically, the current can transfer to other cable by routing on the capacitance of 2 cables. This capacitance completes the circuit that's why you can measure voltage even though it should't have.

Solution is to reduce this current cost by capacitance by placing resistance.

Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#16

Re: Voltage Leakage

09/08/2011 1:19 AM

Actually reduce the voltage across the coil so that it will be less than the hold in voltage.

Design of a shunt resistor to limit the voltage across the coil. That's the solution.