May I ask some help from fellow electrical practicioners. Recently we have an upgrade project with our Water Treatment plant using PLC and HMI (HumanMachine Interface). What we did is we include some indicators not related to Water Treatment Plant like indication of Standby generator status like "Run" "Fault" & "Ready". Those indications were display in LCD Monitor thru PLC. The input to PLC came from external relay which will be turn "on" by Generator local relays. We used a shielded cable with the following specifications:15 cores x 2.5 sq. mm, 500 volts shielded, pvc/pvc, 30 degree c. the supply voltage of the relaycoil is 220 VAC, 60 Hz coming from control transformer located at the PLC control Panel. the distance between Generator panel & PLC panel is about 50 meters. Now my problem is; their is a leakage voltage ranging from 80 volts to 120 volts among wires in the cables when suppose to be only 1 wires is live and the other should have no power unless the intended relay in generator is energized and close the contacts. we already megger the insulation between wires and it is all infinity. the cable is lay in the wall thru PVC pipe and about 10 meters is layed in cable trays and mixed with other cables having voltage of 380 volts for motors supplies. May you help the probable cause of this leakage which result a ruttling of our relays that give input to PLC.