How a marin genset is earthed ? similarly how a huge dumper which havs DC genretor and traction moteres are earthed ?
Re: Genset earthing
09/07/2011 12:46 AM
If done at all, a marine genset would be grounded/earthed to the vessel's hull. Similarly, mobile equipment would be grounded to its chassis/frame (and possibly to a drag chain).
Re: Genset Earthing
09/07/2011 10:17 AM
are you reffering to star connection of generator winding. . normally for marine genset use 3 phase 3 wire and star point is not grounded
Re: Genset Earthing
09/07/2011 9:30 PM
if you have a star connected generator you could have its neutral grounded to the vessel or you could use an impedance ground to limit the current entering your generator neutrals in cases of a line-to-ground fault...but, your the size of impedance should be calculated first...
take care of your seconds and the minute will take care of itself..