Level Switch Contact

09/07/2011 4:09 AM

Please tell me why in level switch (high) contact is taken in NC, can I use NO ? Is some thing called Fail Safe in this case, please explain.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Level Switch contact

09/07/2011 4:20 AM

It sounds like it's designed to be fail safe. E.G if the wire gets cut/pulled off etc this will show as a high level.
Bottom line is you can do whatever you like if you are designing the whole system, but if you are interfacing to an already existing system you need to wire it the way it's designed.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Level Switch contact

09/07/2011 4:26 AM

It is an important principle that the safe condition is a maintained signal and the alarm condition is an absence of signal. This way, were there to be a fault in the wiring, supply or equipment, the condition will show as an alarm. The principle is called "fail-safe".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
2
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3

Re: Level Switch Contact

09/07/2011 9:39 AM

A lot of first time posters this morning with text book questions.

Exam week coming up?

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Good Answer (Score 2)
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#4
In reply to #3

Re: Level Switch Contact

09/07/2011 6:26 PM

And, so it seems

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5
In reply to #3

Re: Level Switch Contact

09/07/2011 10:30 PM

it would seem so.. they gotta remember.. Red to Red...Green to Green and blue to bits!

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#6
In reply to #5

Re: Level Switch Contact

09/07/2011 11:21 PM

LMAO!!

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #5

Re: Level Switch Contact

09/19/2011 6:11 AM

PMSL.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#7

Re: Level Switch Contact

09/07/2011 11:49 PM

The question goes to the hearth of the specification of the serial current loop.

4 mA / 20 mA for the two digital states. Any current at all means the loop is alive. But, deviating much under 4mA means resistive problems, deviating much over 20mA means short type of problem. I leave signal level deviations inbetween for you to work out. They are there.

As you see there is more, than simple NC or NO. Two same switches? Two opposing switches? Min/max currents monitored? The monitors monitored?

Failsafe circuits are a fascinating area, but you need the temperament for it. And tons of patience.

Register to Reply
Guru

Join Date: Jun 2009
Location: Bangalore, India
Posts: 725
Good Answers: 24
#8

Re: Level Switch Contact

09/08/2011 12:27 AM

One reaon could be that most level switches are used to fill a tank when the level is low. An NC contact will come on in this state and go off when the level goes high.

__________________
bioramani
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#9
In reply to #8

Re: Level Switch Contact

09/08/2011 11:57 AM

bioramani, your answer is best.

For filling a tank, the NC would drive the fill solenoid coil when the level is low.

For pumping out a tank (i.e. sump pump, sewage lift), the NO contact would turn on a pump or drain solenoid when the level is high.

A single device with either NO or NC will not necessarily provide "fail safe" as the device could fail so that the contacts are always closed (stuck float, welded contacts, etc.) or always open (broken lead, stuck float, dirty contacts, etc.). Determining which failure is safer requires knowing more about the system. A truly safe system requires redundancy and a means to detect and alarm the disagreement so that the failure can be repaired before a second failure occurs.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#10

Re: Level Switch Contact

09/09/2011 2:48 PM

In any switch being used, if the mechanism fails and you are using NO you will not detect the failure, if you use NC and the switch opens it means either it reached its trip position or if failed, in either case the trip will actuate correctly

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#11

Re: Level Switch Contact

09/09/2011 11:00 PM

Hi Imartin,

Fail safe is very important, I did read some where that the reason for the Chernobyl's Disaster was due to non fail safe wiring, but can't remember where.

For instance if we relied on a switch closing to stop a machine and the wire had been broken for what ever reason the machine would not stop.

If we used a NC contact and for any reason including that the circuit was opened to stop the machine it should stop, this is the reason that stop buttons are usually NC in there non active state.

It all depends on your application as to how use your level sensor, for instance if you want to fill a tank and stop it at a fill level then use the NC contact, but if you had an application that when the level has become high you need to pump the material out of the tank you could use the NO contact. This would also depend on the application that it was used in.

If the application that it is used in could cause harm to people, you then have to evaluate the harm that can be done and it becomes a Category Standard up to Cat 4 you then have to install a safety relay of the approved ratting. This would mean more control wiring and correct installation, if this is required please take advise of the a person familar with this situation.

Best Regards

Joe

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#12

Re: Level Switch Contact

09/10/2011 9:46 AM

When electrical switches fail, they tend to fail open more often than fail shorted. Therefore, it makes sense to design a safety shutdown circuit in such a way that the most probable failure mode (open) initiates a shutdown to avoid a "dangerous undetected fault" condition.

In the case of your high-high level switch, it is wired NC so that it will open when the level gets too high. If the switch happens to fail (open), then the control system will see that fault as a high-high level condition and also shut the process down.

The basic rule of fail-safe system design is to design the system in such a way that the most probable equipment failure mode(s) initiate a safe shutdown.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bioramani (1); brich (1); dj95401 (2); Joe Sparky (1); KJK/USA (1); leveles (1); PWSlack (2); Snave (1); tonykuphaldt (1); user-deleted-1105 (1); vargaalex (1)