Drying Out an Alternator

09/11/2011 11:58 AM

hello,

we have been facing a problem of drying out of an alternator. Actually i have loaded the alternator by coupling it with 17 kw motor & d output of alternator was given to the heater for dissipation as a load on motor.

But after increasing the load< 100%, on motor the alternator had a spark at the end of its fan cover after 5 min.

I think the problem of sparking was due to megger fail. Bt i had run d alternator on no load for 15 to 20 minutes and if megger was already fail then sparking would have occured during no load condition.

Now i want to dry out the alternator for complete confirmation of the winding burn out, since when d alternator opened there were no signs of winding burn out.

The alternator is too large so as to keep it in oven after dismantle. i had opened its fancover side. and i want to dry it out.

Plz tell me any simpler process to dry it OUT.

I cant use bulb method since there is no space inside the alternator to keep the bulb.

I have applied one technique : i kept an heater of small size outside the fancover and the heat generated by the heater is blown through the alternator wid the help of fan which is kept at the back of the heater. bt wid dis small heater it will take long time to dry it out.

Plz suggest me a good soln.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: drying out of alternator

09/11/2011 12:04 PM

"Plz suggest me a good soln."

I suggest the use of whole words and spell check. That helps here every time being they are both free here.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Drying Out A Alternator

09/11/2011 3:31 PM

I don't see how drying the alternator out is going to help you if the winding has in deed gone open circuit during an insulation resistance test failure.

If the winding is still fine and you just want to dry the motor out, and you don't have a big enough oven, you could just disassemble the alternator as much as practical and then build a small enclosure (vented or sealed depending on what drying method you want to employ) around the alternator and use as many home or commercial fan heaters as necessary to blow hor air across, through and around the disassembled alternator (the heaters are not expensive). Keep it simple!

Be careful if you use wood for your makeshift oven.

__________________
jack of all trades
Register to Reply
Member

Join Date: Sep 2011
Posts: 5
#4
In reply to #2

Re: Drying Out A Alternator

09/12/2011 12:25 AM

since its monsoon season it is going to show insulation failure.

well thanks for ur kind suggestion.

Register to Reply
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#3

Re: Drying Out an Alternator

09/11/2011 11:59 PM

To heat the windings DC will not cause rotation and voltage stress on insulation is minimal.

Some air blown through the alternator will carry away the water vapour.

Rectified AC will cause minimal winding ripple and modest extra insulation stress.

Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#5

Re: Drying Out an Alternator

09/12/2011 12:59 AM

"Plz tell me any simpler process to dry it OUT"

You can apply low voltage AC or DC to winding to heat up winding of Generator; this is not simple as keeping heat blowers and heating.

I share my experience here! During 1982 I was working at Bargi Masonry Dam construction project as Electrical section in-charge; due to sudden flash floods in the river Narmada all our electrical panels, motor starters, Tower crane panel, motors, cables, etc went under river mud water for one month. I have dried every thing after cleaning the mud with water jet; more than 600 motors, panels, even cables, etc using "Heat convector's" (heat air blowers) that many people use in Northern India.

__________________
Subramanyam
Register to Reply
Member

Join Date: Sep 2011
Posts: 5
#6
In reply to #5

Re: Drying Out an Alternator

09/12/2011 1:08 AM

yes you are right

Register to Reply
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#7

Re: Drying Out an Alternator

09/12/2011 7:29 AM

A usual approach would be to try to get heat into the winding without applying a lot/any load. If it were possible to bottle up the generator (block the cooling passages) and run the unit at speed no load the heat of windage may be enough to dry things out.

The other option is to hook up a welding machine and warm it up with current. I don't remember the exact details of how we did this so I would suggest getting someone with prior knowledge before attempting this method. You will need a welding machine and a shunt at the minimum.

Of course this is formulated with entirely too little information, such as what happened to cause the problem, what electrical tests are prompting you to believe that the winding is wet, what is the history of the problem ,etc.

__________________
If you fail to follow through, you will fail.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Drying Out an Alternator

09/12/2011 11:10 AM

I'm not sure how big your alternator is but if it has a manual excitation mode and metering then you can try this. Bolt all three phase leads together with a suitably sized piece of buss bar with properly torqued bolts (suitably sized means capable of carrying rated current without overheating). Spin your alternator up to rated speed with absolutely no excitation applied, then slowly (starting at zero field) apply the field until the alternator output is about 90% of full rated current (the terminal voltage will be near zero, after all it's feeding a short circuit!) Monitor carefully for about 8-16 hours after the temperature stabilizes near its rating. You're looking for the temperature to rise due to the fact that full load current is circulating through the windings. You should monitor the outlet temperature and perhaps the dew point of the cooling air if you have that capability, but the most important thing to watch is that the phase currents are within a few percent of each other and that the temperature of your bolted three phase short circuit connection is not too high. Periodically you should shut the system down and check the PI (polarization Index) and/or the insulation resistance with the appropriate instruments. When it's where you want it to be you're done.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

chauhan deepak (2); jack of all trades (1); kvsubramanyam (1); otha (1); RAMConsult (1); tcmtech (1); Zaf (1)