Differance Between Single Core & Muilticore Cable

09/13/2011 4:04 AM

What the Differance between single core & Muilticore cable

Recently in my project I have termined 6 Sets 4x240mm cable to a Transformer of 1000KVA 380V 60Hz

But presently I doing a project in Jeddah for KAIA air port in that consultant has disapproved the Multicore Cables please define technically what are the difference

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Differance between single core & Muilticore cable

09/13/2011 4:25 AM
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Differance between single core & Muilticore cable

09/13/2011 7:09 AM

Because of the distance and changes in terminology are you asking by core difference in solid single strand or multi-stranded conductor? Or bundled wires in the same jacket? Either way whats the difference the customer has given his disapproval. If you are looking for information to argue his disapproval then you won't get much work that way. Customer though they may not be right must be appeased to think so. Do it his way. If this is a change in the designed as put down on the contract then get it in writing. You should also be looking at local codes if you want to argue the change.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Differance Between Single Core & Muilticore Cable

09/13/2011 10:42 AM

Just for information, what is the primary voltage?

Register to Reply
Participant

Join Date: Jun 2010
Posts: 2
#6
In reply to #3

Re: Differance Between Single Core & Muilticore Cable

09/17/2011 4:41 AM

primary voltage of transformer is 13.8V 60Hz

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Differance Between Single Core & Muilticore Cable

09/13/2011 11:15 AM

I believe that you are asking why some customers will allow multiple parallel conductors per phase while others won't. Ignoring cost differences which are easy to calculate, the engineering reason is based on experience and is more subtle. After all 4 smaller conductors each carrying 500 amps deliver the same 2000 amps as one appropriately sized conductor on a per phase basis. Unfortunately the current doesn't always divide so evenly, especially on very long runs, and is very dependent on having perfectly matched lengths for each of the 4 conductors as well as terminations that are also exactly the same resistance. Why? Because if there is any significant difference in the path (one conductor longer than the others or a termination that is poorly made) then the current will divide unequally and sooner or later the more heavily loaded conductors will become overloaded, overheated and fail. Your customer has experienced this and is concerned with the reliability of his installation.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Differance Between Single Core & Muilticore Cable

09/14/2011 7:09 AM

Before commencing work did the Consultant give specifications for equipment?. Single core cable is easier to handle(bending/terminating/pulling/laying),especially if bending radius is small flexible single core is advisable. Normally in specifications consultant gives,full description of cable. What nationality is he?.