Dear Sir
We had a bus bar of 1250 A LOADED AT 70 % Load. But Temp is too high some around 90c. So how to reduce tempreture?
Pathfinder Tags: Bus bar
Re: bus bar temp
09/13/2011 6:18 AM
  • Reduce the load.
  • Tighten the fastenings
  • Ventilate it better
  • Etc.
Good Answers: 266
Re: Bus Bar Temp Too High
09/13/2011 7:20 AM
First acquire an infrared thermometer and locate the source of the heat. It maybe just as simple as a loose connection as PWSlack refers to tighten the fastenings.
Good Answers: 181
09/13/2011 7:23 AM
Bus bar is under rated! Fit bigger
Good Answers: 69
09/13/2011 9:01 AM
Hi:
If this is the original design and it used to work just fine; then most likely you have a poor connection between two copper plates, which causes the metal to overheat, erode and make it a worse contact 'till it self destructs.
Hopefully you're in time to disassemble it, rectify the surfaces, cover them with Cool-Amp and make a tight connection; and now that you're embarked, replace all isolators and check for clogged water lines as well.
09/14/2011 7:00 AM
Who sized this busbar?. What factors were considered while sizing?. Did they consider ambient temp,ventilation,emissivity/purity of copper,gap between phases/earth etc. Is the load constant or cyclic or with periodic peaks?.
pnaban
09/14/2011 12:32 PM
"...too high ..."
Two words unexpected from an engineer!
Temperature is ___ degrees C
Acceptance criteris is ____ degrees C
Acceptance criteria is from ____ documnet or standard.
Fill in the blanks.
Many technicians and work supervisors come to me with "..too high..."
I hate thermography cameras and handheld infrared temperature measuring devices.
I always ask, is the paint blistered? Is the electrical tap insulation bubbled up?
I'll bet your bus bar ran fine until you implemented a temperature monitoring program, right?