11kV/433V Transformer

09/14/2011 12:17 AM

I read in some books that the maximum capacity of 11kV/433V Transformer is limited to 2000kVA. Is it like that or not?. If it is like that then what is the reason? Is there any reason related to voltage range? Please help me...........

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#1

Re: 11kV/433V Transformer

09/14/2011 1:19 AM

If it is so it is rated for optimum in considering economic,protection and many other facts. Can you calculate rated ampere for transformer having more than 2MVA in its low voltage side?

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#2

Re: 11kV/433V Transformer

09/14/2011 5:38 AM

Not true.The restriction of maximum capacity of 11 kv/433 V transformer depends upon the available maximum rating of LV side Air Circuit Breakers (ACB).

These days ACBs of ratings as high as 6300 A are available.This can meet the requirement of maximum transformer capacity upto 4.5 MVA.

However, the capacity of the transformer is normally selected depending upon the Maximum demand of the substation at the concerned load center.

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #2

Re: 11kV/433V Transformer

09/15/2011 7:12 AM

But then what will be fault current from a 4.5MVA Trabsformer? Can your 6300A ACB break it safely?

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#8
In reply to #6

Re: 11kV/433V Transformer

09/15/2011 8:12 AM

Certainly.

You may see ABB's catalogue for Emax type low voltage ACB model No.E6H/f ,which indicates the rated ultimate breaking capacity under short circuit (Icu) as 100 kA at all low voltages including 415 volts . Fault current from a 4.5 MVA transformer will be less than the above value.

__________________
Learning is a never-ending process.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: 11kV/433V Transformer

09/14/2011 5:57 AM

Economics are a ruling factor. As spradhad said ACB's can be rated up to 6300A but then you have the problem of fault currents on the bus bars and all ancillary equipment related to the system. Multiple lower rated units are a more viable (and safer) option.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5
In reply to #3

Re: 11kV/433V Transformer

09/14/2011 3:09 PM

Multiple lower rated units are a more viable (and safer) option.

As well as being easier to transport on standard roads which have size, weight and height restrictions.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4

Re: 11kV/433V Transformer

09/14/2011 8:05 AM

Is it like that or not?.

NOT LIKE THAT.

If it is like that then what is the reason?

QUESTION NOT APPLICABLE.

Is there any reason related to voltage range?

QUESTION NOT APPLICABLE.

Please help me...........

WHAT HELP DO YOU NEED?

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#7

Re: 11kV/433V Transformer

09/15/2011 7:42 AM
Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); hithuanand (1); jack of all trades (1); soebfatehi (2); spradhan (2); TonyS (1)

Previous in Forum: Why Voltage Becomes Zero During Short Circuit?   Next in Forum: AC Input to Bridge < DC Output! Amazing

Advertisement