09/15/2011 3:15 AM
What are the types of protective relay used in feeder?
Good Answers: 170
Re: Protective relays for Feeders
09/15/2011 6:59 AM
A simple Overcurrent and Earthfault Relay to start with. It could be Definite Time or IDMT.
Add-on could be a short-time or instantaneous over current relay and a short time or instantaneous earth fault relay.
More comments after knowing what type of feeder you want to protect.
Location: ROUEN (in NORMANDY), 120 km from Paris, France, Europe, Earth, Sun Sytem, Milky Way, Universe.
Re: Protective Relays for Feeders
09/16/2011 1:37 PM
WHAT TYPE OF FEEDER (s)? what voltage level?What feeder (s) use (s) ?
An overcurrent relay is good up to 33 kV (in some very few uses). Above and including 33 kV, you need either a distance protection (depending of the length of your feeder) or a differential protective relay. You may have (from 500 kV lines and above) a protection through satelites telecomm...So, what are the use and the voltage level?
Sincerly yours, BRZK.