Earth & Neutral Link

09/15/2011 3:18 AM

The neutral bus bars shall be linked to the earth bus bars. These links shall beremovable. The earth bar shall be a minimum of 300 sq. mm or 50% of phase busbar and continuous throughout the length of the panel.Under no circumstance, a common earth/neutral bar will be accepted.

My question is why neutral & earth should be linked?

why a commom earth/neutral bar should not be used?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Earth & neutral Link.

09/15/2011 6:57 AM

Please note that the neutral and the earth bars shall be linked or bonded ONLY (AND ONLY) at the Source Grounding Point and NOWHERE ELSE.

The neutral and the earth bars shall be linked (though only at the source) to ensure that the earth bar is kept at neutral potential always.

Yes! One can very well use a common Earth/Neutral Bar and it is called the TN-C System and then this bar is called the PEN Conductor. But, the problem is both the system unbalance current as well as the earth fault current would flow through the PEN (Protective Earth & Neutral) Conductor. One wouldn't be able to identify whether it is the unbalance current or the fault current. Thus, fault isolation becomes difficult thus endangering somebody's life.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2011
Posts: 43
#2
In reply to #1

Re: Earth & neutral Link.

09/15/2011 9:09 AM

I concur with electricalexpert, the earth and neutral should be linked at source. Normally speaking installers prefer to connect an earth wire from the MET (MAin earth terminal) to the shield of the main cable, this will eventually be earthed at the earth substation side from the neutral star point. Here now your relying that the electrical supplier's earth is good enough. However some countries do not guarantee that it should be the case and this would be at your own risk. Generally speaking it is advisable to design a TNS system having your own earth through earth electrodes or earth mats.

Some will not always guarantee 0Amps in the neutral feeder. (not the ideal world)

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#3

Re: Earth & Neutral Link

09/18/2011 10:33 PM

Dear all,

In case TN-CS:

Neutral-Earth link is to make neutral and earth equal potential.

In case TN-S:

Neutral-Earth link is to make earth-fault return current pass. Without return current pass, an earth-fault will not be cleared by an MCB or MCCB.

If we have separate Neutral and Earth bars, you can connect neutral wires to neutral bar, PE wires to Earth bar (installation easy). If you need to check the insulation, remove the neutral-earth link, and put your megger probe on the neutral bar (maintenance easy). You can have a common neutral and earth bar at the distribution panel the first one from your power source, if you do not care about installation and maintenance. There will be no Neutral-earth link other than the first one.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); electricalexpert65 (1); RyanC83 (1)

Previous in Forum: Protective Relays for Feeders   Next in Forum: Grounding of Motor

Advertisement