Grounding of Motor

09/15/2011 6:32 AM

Dear all,

I have a 3 phase motor, located 300m away from the MCC. What is the difference if I use 3 cores + E cable, the E is used to 'bond' between the MCC and motor, or I can just use 3 cores cable, and 'bond' the motor to the nearest steel structure, assuming that the steel structure is grounded.

Thanks in advance

Register to Reply
Pathfinder Tags: Grounding of motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Grounding of Motor

09/15/2011 6:52 AM

You may very well "bond" the motor frame to the nearest steel structure (with two seperate and distinct connections) but please ensure that the steel structure is connected solidly to the plant earth grid at all times.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Grounding of Motor

09/15/2011 7:28 AM

Is the cable your proposing SWA? If yes, and the armour is used as the CPC then yes, bond to the local steelwork as well.

But please don't use the steel structure as your only earth return path.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#3
In reply to #2

Re: Grounding of Motor

09/15/2011 7:53 AM

and please don't use the armor of the cable as a grounding conductor . . .

Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#4
In reply to #2

Re: Grounding of Motor

09/15/2011 11:14 AM

@TonyS:

It's not an SWA Cable but PVC Cable.

If I use 3C + E, means that I have to provide 300 m copper that 'bonds' MCC and motor together. Or I can use 3C cable + 4 m of ground cable that 'bonds' the motor and steel structure together?

Would the two give the same result?

Thanks in advance..

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #4

Re: Grounding of Motor

09/15/2011 2:45 PM

Safety costs money unfortunately.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Grounding of Motor

09/16/2011 6:31 AM

....while a lack of safety costs considerably more. Like, lives, for instance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Grounding of Motor

09/15/2011 1:44 PM

As mentioned many many times in this forum, you need to check the local rules in force where this is located.

If this was in Canada, a seperate bonding conductor would be required.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#8

Re: Grounding of Motor

09/18/2011 3:04 AM

Your two conditions still satisfy the requirement that motor should be grounded. The difference between the two is the flow of effective ground fault return to facilitate the operation of your protective device. I prefer additional E copper wire than steel structure because copper wire is more conductive than steel.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#9

Re: Grounding of Motor

09/18/2011 9:41 PM

Dear all,

In NEC, 3core without EGC (Equipment grounding conductor) is prohibited. So, in USA, you must use 3 core + EGC.

In IEC, you have more freedom, you may have 3 core + PE cable.

If you do not want to spend for the additional PE core, you may bond your motor body to the nearby earthed steel structure. To keep your system TN-S, the bonded steel structure must have metal connection with your substation or your neutral of the transformer. If you are not sure of this metal connection, you may select TT system, where your motor can be earthed with local earthing electrode, in your case, nearby steel structure. However, you must ensure the protection circuit will trip in case of an earth fault at the motor, this may require earth fault protection at the motor starter.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

"Almost" Good Answers: