Previous in Forum: 11KV Motors   Next in Forum: 230VDC to 10VDC Converter Circuit 5 Amp Intermittent
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did
IR Test Voltage Selection
09/21/2011 3:44 AM
How can I select the test voltage for Insulation Resistance test according to the voltage rating of the Device Under Test.
If you can't find a way, make one........
Re: IR Test voltage selection
09/21/2011 4:00 AM
By following the procedure and using the equipment in accordance with the test protocol document, filling it in with the results.
Good Answers: 12
09/21/2011 6:45 AM
LV cables, motors, etc 500V; isolation transformers 5000V; and so on!
Subramanyam
Good Answers: 181
Re: IR Test Voltage Selection
09/21/2011 8:00 AM
They will all have manufacturers recommended testing procedures.
Good Answers: 244
09/21/2011 10:07 PM
It is defined in IEEE 43 or IEC 60085-01.
See this link http://www.plantservices.com/articles/2003/135.html
- MS
Good Answers: 170
09/25/2011 12:09 PM
Refer IS 732.
electricalexpert65 (1); kvsubramanyam (1); msamad (1); PWSlack (1); TonyS (1)