15 MVA Power Transformer

09/26/2011 11:24 AM

Hello,

1. Can u guide me which is the preferred vector group for 132KV/33 KV Power transformer ? its rating is 15 MVA and application is Industrial ,this trafo will feed power at 33 KV to 1 no. of 10 MVA furnace Transformer and 2 Nos of 2.5 MVA Auxiliary Transformers

2. If Ynyn0 is selected then can the both side(132 KV and 33 KV) Neutral connected to common Substation Earth Grid??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Sep 2011
Posts: 6
#1

Re: 15 MVA Power Transformer

10/06/2011 11:55 AM

If you are connecting the transformer to a utility chances are that you are going to be restricted to a Delta secondary. This is because the utility does not want to deal with zero sequence currents, from earth faults and tripen harmonics, from your side. Therefore a Ynd11 or Ynd0 is most likely.