Busbar Calculations

09/26/2011 2:54 AM

How to calculate size of copper busbar strip required to carry 6000A DC and 6V for electrochemcial application ?

Thanks

Vinith

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Busbar calculations

09/26/2011 3:10 AM

Use the "search this forum" feature on the right hand side of the screen.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Busbar calculations

09/26/2011 3:34 AM

Total shot in the dark: 25mm x 150mm.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#4
In reply to #2

Re: Busbar calculations

09/26/2011 5:07 AM

Is it the thickness X width ...waht you have mentioned ?

If so is there any chart mentioning busbar carri ying above 5000 A current either in copper or aluminium

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Busbar calculations

09/26/2011 5:10 AM

What else would it be, other than thickness and width?

(And it's copper, as mentioned in the OP; rather than aluminum, which was not mentioned.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#6
In reply to #5

Re: Busbar calculations

09/26/2011 5:17 AM

As copper is told it cant carry above 4500A ....My requirements needed upto 6000A so will there be problem using copper

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Busbar calculations

09/26/2011 5:30 AM

Then make it wider and/or thicker, or two busbars in parallel.

There have been many threads about this on CR4, oftentimes mentioning 1100 amperes per inch2 ≈ 1.7 amperes per mm2 for copper. There is some variation depending on surface area and ambient temperature. For better heat dissipation, if needed, you could go thinner but wider.

Google "busbar calculation" or "busbar area" to discover more.

If you want to be fancy (least area), you could use silver....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#9
In reply to #7

Re: Busbar calculations

09/26/2011 6:58 AM

What should be the heat calculations for 1 in X 6 in Copper busbar ?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#19
In reply to #6

Re: Busbar calculations

09/27/2011 10:57 PM

As copper is told it cant carry above 4500A ....

Who sold you that bovine output? i have worked with 180000A copper busbar in a chemical plant....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#20
In reply to #19

Re: Busbar calculations

09/27/2011 11:58 PM

Hello Sir,

Can i have your contact number am Vinith Gandhi R from coimbatore,Tamilnadu....B.tech.Electrochemical Engineering.....I like to have somw word with you

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#21
In reply to #19

Re: Busbar calculations

09/28/2011 7:49 AM

That is a beautiful bit (lot) of copper work

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster #1
#3

Re: Busbar calculations

09/26/2011 4:05 AM

should it hurt bad to touch the busbar with dc supply? if no, may be I touch today.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Busbar calculations

09/26/2011 6:48 AM

I've used 3/8 X 8" for 4000A so go for 3/8 X 12"

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#10
In reply to #8

Re: Busbar calculations

09/26/2011 7:02 AM
Width6in152.4mm
Thickness1in25.4mm
Copper Ampacity1000A/sq.inches
Current carrying capacity6000

Is this correct ?

if so what would the heat generated for this sized copper busbar ?

Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#11
In reply to #8

Re: Busbar calculations

09/26/2011 7:03 AM
Width6in152.4mm
Thickness1in25.4mm
Copper Ampacity1000A/sq.inches
Current carrying capacity6000

What is the heat calculation for this busbar size ?

Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#12

Re: Bus-bar calculations

09/26/2011 7:41 AM

As i mentioned it is 6000A DIRECT CURRENT with 8 volts ......

Operating Temperature : 32oC

Process : Electrochemical

Material of interest : copper

Conditions: The is no voltage fluctuations as it is a potentiostatic rectifier

Has to be welded to Nickel Electrodes

Help me out in

1.Size calculation

2.heat generation formula

3.insulating the bus-bar

4. how to take connections from busbar to electrodes ? Through whar king of wires ?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #12

Re: Bus-bar calculations

09/26/2011 1:51 PM

You are obviously not qualified for the job you seem to have. Any first year apprentice wireman can figure this out.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Aug 2011
Posts: 15
#15
In reply to #14

Re: Bus-bar calculations

09/27/2011 2:21 AM

Sorry am an Electrochemcial Engineer am not as much as you in Electricals

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13

Re: Busbar Calculations

09/26/2011 9:11 AM

You asked this same question on 12-08-11

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #13

Re: Busbar Calculations

09/27/2011 5:54 AM

Were the answers the same?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Busbar Calculations

09/27/2011 7:59 AM

So 7/.029 is too small, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 15
#18
In reply to #17

Re: Busbar Calculations

09/27/2011 8:08 AM

Dear PWSlack,

Can you explain me clearly :O

Thanks

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#22
In reply to #18

Re: Busbar Calculations

09/29/2011 10:44 AM

Until "you" can explain yourself clearly how are we supposed to explain "you" to yourself clearly?

__________________
The reports of my death are greatly exaggerated.
Register to Reply