How do I make RS 485 Communicate with Delta DVP-12SA PLC?
Pathfinder Tags: RS 485 Communication
Re: RS 485 Communication
10/01/2011 9:34 AM
Click here.
10/01/2011 10:55 AM
Most PLC's use the RS-232 port for programming. The listing of PC/PLC cables in the instruction sheet infers that the COM1 port is RS-232 for programming with either the handheld programmer or the Windows program.
This model CPU can handle Modbus ASCII and Modbus RTU over RS-485. It isn't clear whether the RS-232 port is dedicated to programming only, but it is clear that it talks Modbus over the RS-485 comm port 2.
If the question is really, "how do I get a Modbus master to communicate via Modbus RTU/ASCII with the DVP-SA via its RS-485 port?" then check out the instruction sheet for Modbus communication:
http://www.delta.com.tw/product/em/control/plc/download/manual/RTU-485_instruction_tse.pdf
There also appears to be a multipage step by step Modbus instruction guide here:
https://files.pbworks.com/download/QR18YM7PTw/keltsouth/14108278/DVP%20communication%20Protocol.doc
The PLC is a Modbus slave, so an external Modbus master is required to query or poll the PLC.