Transformer

10/02/2011 10:21 PM

sir,

what are the precuations to be taken before energising a 250 KVA oil type,11KV/440V transformer of a Unitised sub station and how to check the transformer oil is good or not.

Experts please give me the answer

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Transformer

10/02/2011 10:42 PM

Please follow the following

1) The test and commissioning procedures set out by the transformer manufacturer (including reviewing the tests they should have already done at the factory when they made it).

2) The test, commissioning and operation procedures set out in the sub station manuals (and associated documentation)

3) All relevant and applicable local electrical and safety standards (which vary from country to country)

It doesn't sound like you know what your doing (unless this is a homework question). Please leave this sort of testing to qualified professionals to minimise the risk of injury or death.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#3
In reply to #1

Re: Transformer

10/03/2011 2:00 AM

Yes you are right. There are several test to be conducted by the manufacturer before dispatching the transformer. Test reports run in to several pages.

__________________
Subramanyam
Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2

Re: Transformer

10/02/2011 11:49 PM

Meggar transfomer for good insulation.Do a breakdown voltage test for oil provided the oil has good properties.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Transformer

10/03/2011 7:05 AM

For 250kVA, I would suggest the following pre-commissioning tests only:

i) IR Value (HV to Earth, LV to Earth & HV to LV) (Use a 5 kV Insulation Tester for 11kV Side & a 1 kV Insulation Tester for the 433V side)

ii) OIL BDV (Must be more than 35kV)

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5

Re: Transformer

10/03/2011 8:30 AM

In India, there are guide lines given by IS standards - Tests to be carried out on site prior to charging of the transformer, irrespective of the tests carried out on shop floor by manufacturer, some of these are....

1. Transformer Oil test - BDV test - > 60 KV

- Moisture content test < 30 %

- Specific resistivity test > 50000 Meg Ohms for new oil

2. Transformer Vector Group & Magnetic Balance Test

3. Transformer Ratio Test

4. Megger Test

5. Polarization Index of Transformer Insulation should be >2

Since, you have mentioned the Unitised Sub Station, Other tests for other HT equipments should also be carried out, as specified for those equipments.

Specially,

Over All Megger Test of the INstallation

Over All Earth test of the System

Physical clearances maintained - Interlocks of Door & Switch position etc...

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Transformer

10/03/2011 8:50 AM

Please don't misquote. Can you tell me which IS talks about the list of pre-commissioning tests to be done on power transformers?

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#7

Re: Transformer

10/04/2011 12:48 PM

do u have a USS with OIL ? ?

where are you located?

Register to Reply