A question came up in NY last week on a project we designed. I have a natural gas twin 15,000HP compressor building that is Class 1, Div2, Group D. It is Div 2 by virtue of a dedicated ventilation system. There are skid panels that are labeled Class 1, Div 2, Group D. All cabling is MV-105, TC or PLTC in cable trays below the grating deck. It runs from the tray thru Rigid conduit up to the bottom of the NEMA 4 and NEMA 12 panels, all of which are labeled for Class 1 Div 2. I do not think sealoff fittings are required for these conduits. None of the conduits go thru a non-classified area and all are within the same atmosphere. I would like to hear your thoughts on this, particularly where NEC 501.15 applies. Thanks in advance.