Motor Starting Problem with Generator

10/03/2011 1:02 PM

hi all
we have installed 130 kw motor with a star -delta starting system to be driven by 280 kva new generator.but when we test the motor with the gen-set . the motor starts to run but the engine will stop running when the delta contactor closes.( with out the generator breaker tripping ),
the geset supplies only the motor no other load
the altitude here is around 2400 above see level.but i have seen on the generator manufacturer catalog it says it can work with the above stated rating without any deration for up to 3000m above see level.

is this the rating compatibility problem b/n the generator and the motor.
can it be adjusted without changing both machines.

best regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Oct 2011
Posts: 12
#1

Re: motor starting problem with generator

10/03/2011 1:11 PM

sorry the motor is induction motor

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: motor starting problem with generator

10/03/2011 1:26 PM

Load on motor at start up? Time adjustment for delay of delta switch over?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: motor starting problem with generator

10/03/2011 1:52 PM

"...but the engine will stop running when the delta contactor closes"

When a Star-delta starter transitions from Star to Delta, there is a phase shift that occurs which can cause electrical and then mechanical transients that can be very dangerous to electrical and mechanical systems, such as generators feeding them. Star-delta starting is not a great way to start a motor that is being powered by a portable generator for that very reason, and your genset mfr may have added protection against these potential issues. It's better to use a solid state soft starter or an Autotransformer starter, they are much easier of the genset.

Before you can go further, you must determine what it is that is telling your engine to shut down. If the breaker is not tripping, then there is some other sort of current or voltage protection device somewhere that is giving a "Kill" command to the engine throttle control. Without knowing anything about that system, you are going to be chasing ghosts.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#4

Re: motor starting problem with generator

10/03/2011 5:35 PM

Not a big problem, just increase more 2 seconds time at star condition.I believe it will help you out. And monitor the ammeter,voltmeter readings while the starter is shifting from Star to Delta.Another possibility can be if the readings are abnormal when changes to delta then must do check your delta contactor's contacts either latching properly or any demages are there, check it Last option is that go for softstarter or VFD.

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5

Re: Motor Starting Problem with Generator

10/03/2011 11:40 PM

1) While change over between star to delta, the current change to be smooth, this depends on setting of star delta timer, then there will not be any jerk and transition current will not affect the engine.

2) For any electrical transition current problem or voltage dip problem only the DG breaker should have tripped-Please examine

3) If the engine trips please findout the reason,the engine should not trip,

Normally the engine trips for the following abnormal conditions:

a) Low Lub oil pressure

b) High engine water temperature

c) Over speed

d) Low engine fuel Pressure

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Motor Starting Problem with Generator

10/04/2011 12:51 AM

What type of motor is it(design A,B,C,D etc), determine starting kVA/hp?. If within limits check the engine,check cable size from gen to motor and other electrical parameters too.

__________________
pnaban
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7

Re: Motor Starting Problem with Generator

10/04/2011 11:14 AM

What is the driven equipment and how it is connected to the motor?Star delta or any starter does not reduse starting current as is commonly mis understood even by engineers some times.It only reduses the time for which Starting current persists.Pl let us have load details .Only then a proper analysis can be carried out.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Active Contributor

Join Date: Oct 2011
Posts: 12
#8
In reply to #7

Re: Motor Starting Problem with Generator

10/04/2011 1:05 PM

Dear all

thankyou so much for your fast and good answers.

based on your suggestions i have told the technicians there at the site to do some of the suggestion you gave me and

when we tried to increase the time on the timer we have found out the engine stops after the voltage and frequency drops before changing to delta ( within two or three seconds before the motor reaches its full speed while it is on the star connection) i.e we were mistaken earlier to say the engine stops when the starter changes to delta.

I am going to the site in the remote area 500 km from where i am now,the day after tomorrow to check the last possible options and make the last decision

do you still think it is possible to adjust the generator or the motor starter so that we can use the existing system?

or do we have to change the star delta starter with the solid state starter or vfd starter?can this starter work ?which one is better for this problem?

If this is not possible we are planning to change the generator which will be very expensive.

Some one have suggested me to start the generator and the motor all together .that means i will change the starting system so that when the generator starts will automatically stars together.so that this will have the same effect as the soft starter with reduced voltage staring system .do you think it will work?

I would be glad to receive all the possible option which i can try at the site .

best regards

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#9
In reply to #8

Re: Motor Starting Problem with Generator

10/04/2011 2:37 PM

Try by reducing the timing between star and delta.

Please connect the motor to the mains and adjust the timer for smooth transition.

then connect the motor to the generator source and try.

The starting current of the motor should not be greater than 200 % of the Generator full load current, as a general rule.then this problem may crop up.

Further in your case there will be deration due to altitiude.

If the problem persists then you may have to change the starting method of the motor to soft starter.

Also let us know the cable size between the generator and the motor.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#11
In reply to #9

Re: Motor Starting Problem with Generator

10/05/2011 2:49 AM

Pl tell us what is the driven equipment.From what u say it appears to be a fan.There are simple solutions once we know the driven equpment.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12
In reply to #8

Re: Motor Starting Problem with Generator

10/05/2011 5:13 AM

Why don't you try a closed transition star-delta starter?. Still you didn't tell us what is the load connected to the motor.

__________________
pnaban
Register to Reply
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#14
In reply to #8

Re: Motor Starting Problem with Generator

10/06/2011 10:54 AM

Maybe with the existing arrangement your only chance is to reduce the star delta timer IF the motor is already at speed but not in delta already. If you are still in STAR and the motor has load the current will be high (is this when it trips?), changing to DELTA will reduce this IF you are already pretty well at full speed. Basically, as soon as you are at speed, change to Delta.

If this does not work, the certain solution should be VFD which would start within much, much lower currents whatever the load (you don't specify what load you have during this start phase).

If VFD, check with generator manufacturer for % load which is allowable and if OK then you can use the VFD. I would strongly advise you to use DC and AC reactors to reduce harmonic currents so this is more suitable for the generator windings. The DC reactor has most impact so make sure this is not minimal specification as some suppliers recommend.

If you know load characteristics under starting, you can also consider the soft start which may well be OK too, then you have no harmonic problems when at speed.

In my experience, the VFD is a sure bet, the soft start is less certain from a generator trip viewpoint.

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10

Re: Motor Starting Problem with Generator

10/04/2011 2:45 PM

OP, the problem may require no more than some governor tuning. You have not described the nature of the load on the induction motor but I suspect it is rotary with a high moment of inertia and/or starting torque. A clue as to what is happening is your statement about the gen-set tripping a few seconds after the motor has accelerated but just before the transition.

Here's what may be happening, by increasing the start time you have accelerated the load beyond the point where its speed-torque curve crosses above that of the generator, thereby quickly unloading it. This transition can take place very rapidly and has the effect of rapidly unloading the prime mover which will then throttle back to prevent overspeeding.

Think of it terms of driving a car up a very steep hill, you floor the throttle to maintain speed and climb the hill, but when you reach the top and see that it's almost straight down on the other side you immediately pull your foot off and hope that the engine goes from wide open throttle to idle without redlining or stalling. There's probably a governor setting for minimum idle speed, try boosting it and see if that cures your problem. Think about it when you're on your drive there.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Active Contributor

Join Date: Oct 2011
Posts: 12
#13
In reply to #10

Re: Motor Starting Problem with Generator

10/05/2011 12:20 PM

oh sorry for not telling u the load type

the motor is used as a surface pump for water

best regards

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#15
In reply to #13

Re: Motor Starting Problem with Generator

10/07/2011 8:53 AM

Pl furnish details .Is it a centrifugal or reciprocating pump.In any case a simple solution will be intoduce a fluid coupling between the motor and generator which will allow the motor to start practically unloaded.A scupe type will be better.Secondly are u starting the pump with discharge valve closed or openIf close the discharge valve and slowly open as the motor shifts to delta you may not have the problem.In that case u can avoid fluid coupling too.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Active Contributor

Join Date: Oct 2011
Posts: 12
#16

Re: Motor Starting Problem with Generator

10/11/2011 9:13 AM

Dear all

here are the result

first i have adjusted the potentiometer on the AVR (UFRO) .then the generator starts and run the motor properly .it changes to delta without any problem then after it works for one hour pumping water we stopped the generator and restart it .but at this time the generator takes the load but after 4 to 5 seconds the current starts to raise and the overload relay starts tripping before the connection is changed to delta .after observing this problem i reduced the time on the timer after that it starts working properly.I think the last problem is due to the back pressure from the water in the pipe.

thank you all again

best regards

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Motor Starting Problem with Generator

07/04/2024 3:36 AM

If none of the above solves the problem, then call the <...gen-set...> manufacturer and arrange a site visit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: