Substation Related

10/04/2011 6:53 AM

Hi all,

This is regrading one of the projects we are doing in India. There is a substation of 220 KV / 11 KV with two incoming lines and three no of 40/50 MVA, 220/11 KV trafos.
Bus arrangement is SINGLE BUS WITH SECTIONALIZERS. Due to land and other problems, owners are not being able to lay a part of transmission line from state utility board. There is one existing 132 KV line near by and it is proposed to take a tap from that line and bring it to the plant main substation. With 132 KV line, what changes are required in the substation to ensure smooth operation? I currently forsee the following :

1. PTs for metering need to be change.

2. CVTs to be changed

3. Lightning arrestors to be changed.

4. CTs, Isolator and breaker can work on 132 KV also.

5. What about transformers?

Please reply.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Substation Related

10/04/2011 10:00 AM

You need to explain this better.

Are you proposing the supply the 220KV bus at 132KV?

The main effect on the transformers would be 6.6KV instead of 11KV

I'm confused!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#2

Re: Substation Related

10/04/2011 10:42 AM

what is the vector group of your transformer's and for which company are you working for in india?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #2

Re: Substation Related

10/05/2011 8:22 AM

The second question is irrelevant and possibly commercially and personally sensitive. It would be unusual to find a reply to it here and very unwise to post one.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Substation Related

10/04/2011 11:09 AM

I hope this is a temporary problem.You can lay 132 KV tee off line.But your transformers will not give 11KV..If cost is not factor and u want to start immediately and later on switch over to a regular line buy a 132KV/220KV auto Transformer which will be of sufficient capacity to to meet loads and cheaper.may be 40MVa open all other sections.At best u need buy i breaker ,Measuring CT and PT isolators.You can also lease this system and can result in tax savings

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Substation Related

10/04/2011 2:44 PM

OK, so here are some obvious statements.....

This is a major, MAJOR change.

For one thing, a 220kV transformer won't work at 132kV to produce 11kV, unless you plan on going to the expense of adding 6.6kV/11kV step up transformers. If you think you can just change the 11kV transformer's tap changer to step up the output voltage from 6.6kV to 11kV you are (likely) going to be disappointed.

The other problems are that the bus-work, cables, or anything else related to transporting or measuring the current likely won't work within design safety tolerance parameters if you want to drop the voltage from 220kV to 132kV and also increase the current to get anywhere near the existing design output of the substation.

You can also add any VTs to the list of protection elements that need checking to ensure they will work within the required accuracies and tolerances when operating at the reduced voltage.

I suggest a detailed design review, study and plan for such a major change (which I am sure is what you and your project manager, asset owner, etc are doing).

__________________
jack of all trades
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5
In reply to #4

Re: Substation Related

10/05/2011 2:54 AM

He does not say any where about 6.6KV.From his post his sub distribution voltage appears to be 11 KV.Tap changers can boost or buck by 20%.I think a 132/220KV auto transformer would solve the problem temporarily without altering anything.Yes it will be expensive but not so much if u condider other alternatives and this can work well.

Regards

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Off Topic (Score 4)
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#6

Re: Substation Related

10/05/2011 7:12 AM

By having a primary voltage of 132 KV in place of 220 KV will not only change the secondary voltage to 6.6 KV but will also reduce the KVA capacity of the transformer proportionately since the secondary current capacity will remain same at the original 11 KV level.

It would be worthwhile ( if you have already procured the transoformers) to study the possibility of installing an additional 132 kv / 220 KV transformer so that all the 220 KV arrangements will still remain utilized. Of course as already advised by a friend, this is a very major change and must be studied in detail to get the best practical solution.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Substation Related

10/05/2011 8:24 AM

Hire an appropriately-qualified local Electrical Engineering Consultancy to look at this, and delegate the design to that organisation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: Substation Related

10/06/2011 1:38 AM

Transformers can work. But, the secondary terminal voltage as well as the MVA rating will be lower by a Ratio: 220/132. I don't think this (especially the lower voltage on secondary side) will be acceptable for the system.

__________________
Raghunath
Register to Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#10

Re: Substation Related

10/06/2011 8:18 AM

As I understand Jigu 1985 's problems is that he has a substation built for 220 KV while due to some problems the power that can be tapped from the nearest substation is at 132 KV. So, one possibility that could be evaluated is installing a transformer of 132 kv / 220 kv which will enable him to feed power from a 132 KV substation to his 220 kv substation keeping rest of the things as they are.Only an additional 132 KV bus system will be required in his substation. Or this transformer, if the things permit can be installed in the utility company's 132 KV substation.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jack of all trades (1); muditmah (1); nesubra (2); Priyadarshan (2); PWSlack (2); raghun (1); TonyS (1)