Anonymous Poster #1

Earth Fault, Leakage & Circuit Breaker

10/06/2011 4:03 AM

I have recently joined a switchgear manufacturing company & I have a question regarding why in a distribution board , there is only earth leakage protection & not an earth fault protection. I mean to say is that there are MCB/MCCB + ELCB/ELR in a sub distribution panels and my understanding is that ELCB will only protect after detecting Earth Leakage current (upto 30A). Also MCB doesn't trip on a ground fault. so during a phase to ground fault, does the elcb provide protection for such large faults?

The elcb principle states that whenever the vectorial sum of phase and neutral currents is non zero (due to earth leakage, earth fault), elcb will trip. But is it safe for an elcb to handle large ground faults?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: earth fault,leakage & circuit breaker

10/06/2011 5:00 AM

Earth leakage equipment works by evaluating the vector sum of all currents passing through it. If this sum is higher than its trip setting, it trips.

Slam dunk.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: earth fault,leakage & circuit breaker

10/06/2011 6:27 AM

There are now devices called "ELMCB"s. These are primarily RCD+MCB combinations, with the ability to sense overload and short-circuit also in addition to earth leakage, maybe capable of interrupting 6 or 10kA.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: earth fault,leakage & circuit breaker

10/06/2011 7:46 AM

The right name for this device is RCBO - Residual Current Breaker with Overcurrent protection.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4

Re: Earth Fault, Leakage & Circuit Breaker

10/06/2011 11:24 AM

where did you encounter an earth leakage current of 30A? or did you mean 30mA?

. . . so when you use an RCBO . . . any earth leakage current higher than the set value causes the device to trip and disconnect the circuit . . . any overload current causes the O/L protection to take over and isolate the circuit . . . any very high current caused by short circuit (or "earth fault") causes the device to trip and disconnect the circuit . . .

the device to be used is selected by the specifier to ensure that the interrupting capacity of the device (6kA or 10kA are common in domestic use) selected is more than or equal to the possible "very high current" in the circuit even when there is a direct short circuit (or earth fault).

Reply
Anonymous Poster #1
#7
In reply to #4

Re: Earth Fault, Leakage & Circuit Breaker

10/08/2011 12:40 AM

i have not encountered anywhere but i have seen a relay with a setting from 0.03A to 30A.

but when u say an earth fault(phase to ground), normal MCB or MCCBs doesnot trip. i have seen in the catalogues of major brands where they clearly mention whether ground fault protection is provided or not. for eg. in schneider electric, MCCB with TM trip unit doesn't have ground fault protection, while MCCB with Micrologic 6 does. and a normal MCB doesnt provide ground fault protection.

Micrologic 6 trip unit is a costly trip unit and is usually not used in SMDB or SDB.

can u please clear my query?

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #7

Re: Earth Fault, Leakage & Circuit Breaker

10/08/2011 1:20 AM

In MCCB with micrologic what is the method used to detect EF?. For other MCCBs too if you connect a core balance transformer or EFR it will trip. Even MCB can be fitted with tripping coil.

__________________
pnaban
Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#5

Re: Earth Fault, Leakage & Circuit Breaker

10/06/2011 11:12 PM

there is only earth leakage protection & not an earth fault protection.

As I understand your above mentioned doubt, so be sure that ELCBs are only for earth leakage protection and MCBs are for short circuit & Overload protection,so the earth fault is also to be considered as Short circuit, therefore If you need to protect a circuit from Earth Leakage + Short circuit then go with the combination of MCB+ELCB.

__________________
There are no shortcuts on the road to a great experience.
Reply Score 1 for Good Answer
Anonymous Poster #1
#8
In reply to #5

Re: Earth Fault, Leakage & Circuit Breaker

10/08/2011 12:52 AM

sir can u see my comment no. 7 and help me out?

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Earth Fault, Leakage & Circuit Breaker

10/07/2011 12:44 AM

The arrangement in sub DBs or CUs is ok but did you check main switchboards(MSB) where in some they use ELR with core balance transformer while in others they use EFR depending on Amp rating of incoming CB?. Upto what Amp rating of load (or incomer) ELR is used and why?.

__________________
pnaban
Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Aseer (1); kvsridhar (2); pnaban (2); PWSlack (1); soebfatehi (1)