Unbalance Voltage

10/12/2011 6:32 AM

What is the cause of unbalanced line to ground voltage on secondary side of delta delta connected transformer?

Register to Reply
Pathfinder Tags: transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: unbalance voltage

10/12/2011 6:33 AM

A mismatch in the impedances in each of the phase loads would do it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Unbalance Voltage

10/12/2011 10:31 AM

First of all, it is grossly incorrect to "measure" - the phase-to-grou8nd voltage on the secondary side of a Delta-Delta Transformer. Assuming that the secndary Delta is unearthed, there is no way the delta windings will have a coupling (except a very small leakage capacitive coupling, which, of course, is negligible) to earth. In the absence of any such coupling, the secondary delta winding cannot and will not have a potential difference with ground.

Any reading you get in a voltmeter during any such measurement is superficial.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Unbalance Voltage

10/17/2011 7:04 AM

E.E.65 is right, voltage balance of secondary on such a transformer is not something to bother about. In practice, the LV windings have insulation capacitance to ground AND to the HV windings. So by capacitive voltage division, the HV voltage can throw unexpected voltage into an un-grounded delta secondary.

Real transformers have variations between phases (even by design) and unbalanced input voltage and your voltmeter will respond to harmonic frequencies at which input unbalance may be worse than for fundamental - so balanced voltage to ground is unlikely, rather balance would be exceptional.

The only reason to worry is if one phase voltage to ground is very low - which could be an actual earth fault.

You have not written that your transfo is loaded - loads are often single phase and capacitance and leakage to ground of the phase loads are often unequal because the loads themselves are unbalanced.

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); electricalexpert65 (1); PWSlack (1)

Previous in Forum: RIO Panel   Next in Forum: Transformer Current Density Selection

Advertisement