Previous in Forum: Milliamperes Source Circuit Diagram   Next in Forum: Standard for Choosing Whether Valve will be Fail Close/Open
Close
Close
Close
6 comments
Rate Comments: Nested
Active Contributor

Join Date: Aug 2011
Posts: 10

Flow Transmitter Range

10/16/2011 1:19 PM

Dear,

I would like to know how to calculate a new differential pressure range of a DP type flow transmitter with the following datas.

Existing flow range in DCS = 0-7 Tons/Hour

Existing Differential Pressure Range = 0-250 mBar

New flow range in DCS = 0-15 Tons/Hour

What is the new DP range to be set to the transmitter

Please advice me in this regard

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Active Contributor

Join Date: Aug 2011
Posts: 10
#1

Re: Flow Transmitter Range

10/16/2011 1:42 PM

For Your Information That the transmitter itself has a square root extractor.

Register to Reply
2
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#2

Re: Flow Transmitter Range

10/16/2011 5:23 PM

15 tph is 214.28% of the 7.0 tph design size flow rate of the primary flow element which drops 250mbar at 7.0 tph. 214.28% = 2.1428

Flow rate is the square root of the percentage of DP, where 100% DP is the design size.

Square root of what (x) = 2.1428 ?
x = 4.591 = DP in percent full scale in relation to the design sized 250mbar = 459.1% of 250mbar

250mbar * 4.591 = 1148mbar DP at 15 tph.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Aug 2011
Posts: 10
#3
In reply to #2

Re: Flow Transmitter Range

10/17/2011 9:25 AM

Thanks for the valuable reply

Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#4

Re: Flow Transmitter Range

10/17/2011 10:03 AM

If his answer is so valuable, doesn't Carl_E deserve a GA?

For the casual observer, note that the flow rate increased by slightly more than double, from 7 tph to 15 tph.

But the DP went up over a factor of 4, from 250 mbar to 1148 mbar.

Had the flow doubled from 7 tph to 14 tph, the DP would have gone up by exactly 4x to 1000 mbar, because √4 = 2.

Register to Reply
Power-User

Join Date: Dec 2008
Location: Australia
Posts: 143
Good Answers: 24
#5
In reply to #4

Re: Flow Transmitter Range

10/17/2011 6:31 PM

Indeed he does. Clear, concise and more importantly correct. GA from me.

Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#6

Re: Flow Transmitter Range

10/20/2011 9:04 AM

The basic principle you need to keep in mind here is that the differential pressure is proportional to the *sqaure* of the flow rate, all other factors remaining constant. With double the flow, you're going to get four times the DP.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

ajwinemaker (1); Bud (1); Carl_E (1); panamattam (2); tonykuphaldt (1)

Previous in Forum: Milliamperes Source Circuit Diagram   Next in Forum: Standard for Choosing Whether Valve will be Fail Close/Open