Standard for Choosing Whether Valve will be Fail Close/Open

10/16/2011 11:20 PM

good day sirs,

I would like to ask if there are any standard i could refer to when choosing whether a valve should be configured to fail open or fail closed?

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: standard for choosing whether valve will be fail close/open

10/16/2011 11:29 PM

Depends what the valve does.

Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#2

Re: standard for choosing whether valve will be fail close/open

10/16/2011 11:35 PM

It depends on your application, if it's a Nuke Core cooling valve, fail open, it's a toilet flapper valve, fail closed. What are you controlling anyhow? The application would dictate how you'd want the valve to fail, besides not wanting to fail in the first place.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: standard for choosing whether valve will be fail close/open

10/17/2011 12:35 AM

There is no standard that removes responsibility or liability of an engineer to do their due diligence in designing a safe system. You want things to always fail safe. If your valve can harm people in an opened or closed failure then safety alternatives must be added to mitigate the hazard. Depending on the possible failure circumstance, mitigation can take the form of an automated evacuation warning, a second valve in series or parallel, a separate controlling system or a myriad of other system dependent safety protocols.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Associate

Join Date: Jul 2007
Posts: 26
Good Answers: 1
#4

Re: standard for choosing whether valve will be fail close/open

10/17/2011 1:32 AM

Depends on the process line demand . All it has consider is the Safety / Health / Environmental conditions for the People and the surroundings . Acccodingly a valve is selected for a FO or FC condition , but it has to be the FAIL SAFE condition for the situation.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: standard for choosing whether valve will be fail close/open

10/17/2011 8:12 AM

There is a third possibility: fail in last position.

The HazOp Study will evaluate whether the correct selection has been made in each case.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#6

Re: Standard for Choosing Whether Valve will be Fail Close/Open

10/17/2011 1:03 PM

Wonder what happen to the AP with the OP? I'm just curious to know what they're trying to control?

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#7

Re: Standard for Choosing Whether Valve will be Fail Close/Open

10/19/2011 12:43 PM

There is no specific standard, rather its and operational safety requirement.

Some valves need to fail ope, others closed, others last position and others do not matter.

The process / operations group defines this based on the fail safe mode of operation of the plant.

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dj95401 (2); lyn (1); PWSlack (1); redfred (1); vargaalex (1); Voltamps (1)

Previous in Forum: Flow Transmitter Range   Next in Forum: Telescope Focusing Problem

Advertisement