In reference to say 40/50MVA 33/11kV transformer

How transformer loading is monitored to switch on & off ONAN/ONAF tarnsformer's fans?
Similar to winding temperature monitor.. oil cup & CT?
Or vendor actually do have load monitor (CT & PT inputs wired) with digital output contacts programmable for switching on fans at perticular loads?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: ONAN/ONAF Transformer Fan Switching Controller

10/18/2011 7:48 AM

The most fool-proof method is WInding temperature monitoring.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2011
Posts: 2
#2

Re: ONAN/ONAF Transformer Fan Switching Controller

10/19/2011 7:24 AM

Not sure about load but vendor will provide the digital output from the winidng and oil temperature to switch on and off the fans.