MCB RATING

10/18/2011 3:10 AM

THREE PHASE MCB OF 32A MEANS EACH PHASE OF MCB CAN CARRY 32A. WHAT ABOUT NEUTRAL. SINCE IN 3 PHASE SYSTEM THE UNBALANCE CURRENT WILL FOLLOW THROUGH NEUTRAL ONLY. OR WE CAN SAY IN 3 PHASE POWER DISTRIBUTION SYSTEM THE NEUTRAL CONDUCTOR IS OF DOUBLE SIZE OF OTHER 3 CONDUCTORS (NOT LIKE CONVENTIONAL METHOD WHERE THE SIZE OF NEUTRAL WAS EQUAL OR HALF OF OTHER 3 PHASES).

WHAT ABOUT MCB, NUTRAL IS ALSO RATED FOR SAME CURRENT RATING?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MCB RATING

10/18/2011 7:25 AM

Please turn off Caps Lock; there is no need to SHOUT.

The current in the neutral will never be greater than the largest of the currents in any of the three phases, as it is the vector sum of them.

Installing a circuit overcurrent protection device in the neutral conductor is a practice that falls outside British Standard 7671 and can lead to potentially lethal results.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: MCB RATING

10/18/2011 7:51 AM

If you want to have a "break" in the Neutral Pole too, then you must go for either a TPN or a four-pole MCB. In a TPN or four-pole MCB, the continuous current carrying capacity or the rating of the neutral is the same as that of the phase.

However, in a triplen harmonic rich environment you may have to double-size the neutral for which you may need five pole MCBs. But, I doubt, any such product is available in the market today.

Register to Reply
Anonymous Poster #1
#3
In reply to #2

Re: MCB RATING

10/18/2011 10:21 AM

Triplen harmonics cancel each other out in 3 phase, as do even orders. It's the non- triplen odd order harmonics you need to worry about. But I have no advice on sizing a CB for that, we are not alowed to switch the neutral here in the USA.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: MCB RATING

10/18/2011 8:42 PM

I am surprised at such a grossly "incorrect" comment. The definition for triplen harmonics is "odd multiples of three". And, it is a globally well-known fact that triplen harmonics have zero phase sequence, and thus add up in the neutral as neutral current. This being so, your statement that triplen harmonics "cancel out" each other in the three phases is WRONG, WRONG and WRONG. Also, please note that even the even order harmonics don't 'cancel' out each other, but only their effects are nullified due to what is called "half wave symmetry" effect. And, the non-triplen odd order harmonics, like 5th, 7th, 11th, 13th, etc. have no business with neutral whatsoever. I fear that you yourself first need a thorough learning about harmonics, before posting such incorrect answers here in this forum.

While I agree that in US, neutral switching is not allowed, as the network is TN-C, here in India, we generally follow a TN-S system and hence, neutral switching is very much permitted.

I am deeply worried about such wrong and dangerous advices being posted here in this elite forum.

Register to Reply
Register to Reply 4 comments