Burner Limit Switch Problem

10/19/2011 9:40 PM

Hi,

We are running a conventional boiler (oil fired) with 16 front firing burners.

We are having problems related to air register limit switches open indication.

We have found out that the limit switch cannot withstand the dust and temperrature.

We keep on changing and also eventually jumpering the signal for air register open indication.

FYI, we are using an explosion proof limit switch. Is there anyone in the market that sells heavy duty explosion proof limit switches that can withstand temperature and also a high speed actuator?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Burner Limit Switch Problem

10/19/2011 10:09 PM

Maybe you could mount the limit switches off the the side, on standoffs, or some such way to get them farther from the heat; and then attach extension arms to the registers to reach the relocated switches.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Nov 2010
Posts: 18
#2
In reply to #1

Re: Burner Limit Switch Problem

10/19/2011 11:48 PM

Thanks.

One of the problems we faced in doing so is that there is no space.

The limit switch is close to the burner wall.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Burner Limit Switch Problem

10/20/2011 12:51 AM

Plan B: Put some thermal insulation in the space between the limit switches and the mounting surface.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#4

Re: Burner Limit Switch Problem

10/20/2011 9:08 AM

You could try using an optical limit switch with remote-mount (fiber optic cables transferring light to and from the electronic switch unit) option. Let the mechanism break the light beam to verify position. Remote mounting solves the heat problem.

As for dust, use a purge air nozzle near the fiber optic lenses to keep them clear of particulates.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Commentator
Safety - Hazmat - R&D Engineer/Inventor

Join Date: Apr 2009
Location: South Florida
Posts: 88
Good Answers: 8
#5

Re: Burner Limit Switch Problem

10/21/2011 8:32 AM

The "flame safeguard system" and "combustion controls" are components that are shipped with the "conventional boiler package" hence for liability sake, this is problem that should be corrected by the manufacturer of the boiler or burner. I would put it on them to correct the problem at there expense and expertise.

__________________
masterblaster
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7
In reply to #5

Re: Burner Limit Switch Problem

10/21/2011 1:36 PM

GA

Safety first. Do not re-invent it.

On the other hand, just for the sake of giving ideas: a flexible steel cable link, that will move with the air register as it opens or close, could be used to actuate a remote switch. this will allow you to get rid of the space problem near the boiler wall (as you said).

Suggest it but get the maker/supplier to approve it.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#6

Re: Burner Limit Switch Problem

10/21/2011 12:31 PM

Like Tornado mentioned you can wrap the limit switches in insulation and install some vortex coolers to cool the inside and / or outside of the instrument bodies.

I have seen in some cases where a small box with the sides and back filled with thermal insulation is placed around the limit switch with cut outs for the limit switch arm to go through.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#8

Re: Burner Limit Switch Problem

10/21/2011 11:14 PM

Another option would be a static pressure switch (mounted remotely) sensing pressure of the fan discharge.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: