hi
we have Three gas generator . i want to ask which method would be more suitable and cost effective to cotrol there noise.
1. enclosure on either compressor
2. construction of compressor building having sound barrier walls
Re: generator noise attenuation system
10/20/2011 1:23 AM
Option 2 is probably better, because it will leave better access to the individual generators.
Good Answers: 141
10/20/2011 2:04 AM
In risk evaluation and prevention, the cure is qualitatively processed as follows:
The gas generator noise is the risk as a source.
1. Eliminate the risk by removing, switching off and
2. in your case ISOLATE IT.
You have 3 sources, so finding a total solution as Tornado proposes is OK, when you consider these generators as 1 RISK.
However if you also want to protect the people that e.g. work on one generator while the other 2 are in service, the job isn't done with putting these in one room of a building. 3 sound proof rooms in a building brings us to a treatment of each individual generator.
Rests:
3. Individual protection for each person exposed to the risk.
Considered the worst, and very impractical for a long time. (to avoid when 1. or 2. can be applied)
This is a general safety standpoint, when it comes to prevention.
Cost effectiveness is not always the same road for a short run, but when people start complaining and file for being victimized - professional diseases e.g. ,
the LONG RUN economics might show different.