Use of Separate Neutral Cable

10/20/2011 1:31 PM

In most cases , we need four cable for our star connected 3 phase 4 wire load. But problem is that we often do not have the same diameter four cable cable for this star connected 4 wire load. What we do then is to use three core cable for the three phases and a single core seperate cable for neutral. Now my question is:

Is this techincally OK to use 3core + 1core cable instead of using a 4 core cable for star connected 4 wire load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#1

Re: Use of Separate Neutral Cable

10/20/2011 2:12 PM

Although I have never seen an one core power cable, you can use anything what does not put to risk (yours and) other people's health and property.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Use of Separate Neutral Cable

10/20/2011 2:45 PM

Well yes, you can use single core conductors in a three phase systrem (which I have done once in a special situation) but.....

a) You have to be careful of inductive heating effects created by circulating currents when passing the cables through magnetic metal (such as steel), idealy by passing the cables through non-magnetic aluminium.

and

b) You need to check your local standards to see if it is allowed in your particular application.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Use of Separate Neutral Cable

10/20/2011 3:05 PM

Is the obvious solution impossible to implement?

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#4

Re: Use of Separate Neutral Cable

10/20/2011 4:14 PM

For a test or other temporary installation, I do not see a problem. For any permanent installation if you do not the correct components, buy them.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: Use of Separate Neutral Cable

10/20/2011 11:13 PM

Local code dictates. But the basic idea is, that a neutral have to be able to carry the full current of a phase in the case of a failure. A melted / scorched undersized neutral is no fun.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Use of Separate Neutral Cable

10/21/2011 4:39 AM

If it's star connected, why do you need neutral?

Or are your loads single phase?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Use of Separate Neutral Cable

10/21/2011 11:04 AM

As already mentioned, the problem will be when passing through a metal panel: the single neutral cable must pass in the same hole as the 3 core cable (even is the load is 3 phase, start connected, in case there was a possibility of the neutral carrying some current).

Also, the 3 core cable should not be armoured! the armour could become the host of unbalanced currents when the neutral start conducting some of it!

All this is necessary if you need the Neutral wire for phase to neutral loads !!

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); jack of all trades (1); LAA_Lucke (1); leveles (1); lyn (1); redfred (1); Yuri B. (1)