LT MOTOR

10/21/2011 11:38 AM

largest capacity of motor is used in LT system ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: LT MOTOR

10/21/2011 11:39 AM

Oh, 100kW?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: LT MOTOR

10/21/2011 1:22 PM

Used anywhere in the world?

The biggest I have ever worked on was 1500HP (1,100kW) at 480V. But I just heard that A-B is about to release a new version of their drives that will go to 2,000HP (1500kW) at 400/480V in the last part of 2012, so there must be a market for it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: LT MOTOR

10/21/2011 9:20 PM

Don't put me down for pulling in the cables.

The biggest 415V motor I've worked on was 800HP that was bad enough.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #3

Re: LT MOTOR

10/21/2011 11:54 PM

The 1500HP was connected with flexible bus, the braided kind not the "flexi-bar" stuff. Installation wasn't that difficult, but I wasn't paying the bill for that bus. The soft starter was right next to the motor (ID fan on a giant boiler for a biomass generator) so it was at least not a long distance. It was the only large motor at the plant so they didn't want to run it at MV because it meant extra switchgear and another transformer.

I know what you mean though, I did a 900HP 480V wood chipper with cables (I have a picture somewhere that I'll post if I ever find that box). THAT was a lot more difficult...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #2

Re: LT MOTOR

10/21/2011 11:42 PM

What is the advantage of having a LV motor of such high capacity instead of having a higher voltage(4.16/6.6/11/13.8kV) motor?.

__________________
pnaban
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #4

Re: LT MOTOR

10/22/2011 12:03 AM

No advantage really, but for someone who doesn't have any other MV equipment, it can be expensive to add MV distribution equipment to add just one unit and also daunting to have to have a maintenance person on-site who has MV qualification.

On one pump station I did, the pumps (3) were 700HP and they did go with 4160V because they felt is was less expensive, but then the 2 maintenance electricians hit them up for a sizeable raises after they paid for them to go to classes for being qualified on MV work. 6 months later one of them quit because being MV qualified, he was in high demand with other plants. The water dept. engineers said later they regretted that decision.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: LT MOTOR

10/23/2011 9:37 PM

I have worked on 1500HP, 415V AC Motor.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); JRaef (3); pnaban (1); PWSlack (1); TonyS (1)