Fire Protection of Power Transformers

10/24/2011 1:33 AM

Fire Protection of power transformers: We have 2 oil transformers each of 1 MVA ,33/0.433 kv rating and oil capacity of 927 litres.Do i need to have the firewall between 2 transformers.What is the minimum centre to centre space between the transformers so that barrier wall is not required?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Fire Protection of power transformers

10/24/2011 1:40 AM

Yes, no, maybe.

It depends where you are. With no information to go on, I'm lost. So are you.

British Standard, NEC, who knows. Maybe you're a BMOC.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Feb 2011
Location: Dubai, UAE
Posts: 63
Good Answers: 7
#2

Re: Fire Protection of power transformers

10/24/2011 4:18 AM

Oil filled Transformers are susceptible to catch fire and in case a transformer catches fire anything in the vicinity will get engulfed.

Codes require a minimum distance of one meter between the fire wall and transformer but leave it to you to judge the separation between the transformer and the surrounding objects should there be no wall.

Having said that, it is you who would let us know that if there is a separation of xx meters between the two 1MVA units, in case of fire on one the other will not have any adverse effect.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Fire Protection of Power Transformers

10/31/2011 8:44 PM

Please refer to the Indian Electricity Rules, 1956. Rule No. 64 (2) (e) (i)

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

A.A.Khi (1); electricalexpert65 (1); lyn (1)

Previous in Forum: Speed of a Permanent Magnet Synchronous Motor (PMSM)   Next in Forum: Condenser Testing

Advertisement