Condenser Testing

10/24/2011 2:25 AM

Sir,

I have an AC- ONE TON -. I have a doubt Its conderser has gone. On the fact it is written - 35 micro farad. How to test ( with a multi meter etc ) whether isgone or ??? . The shop keeper says - sir - bottom is slightly bulgy - so it has gone . But how to test it ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: condenser testing

10/24/2011 8:09 AM

Measure ohms between the two terminals with a multimeter. The value will rise exponentially. If, after a suitable delay, the figure hasn't gone off-the-scale high end ohms, the item is faulty.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#2
In reply to #1

Re: condenser testing

10/24/2011 4:54 PM

That's not the way I do it. I take my meter in ohms setting and connect to the two contacts (with the cap disconnected from the wiring) (to be safe, connect the contacts together for a second to discharge the cap) (a cap is the same as a condenser for this thread) anyway, the meter will jump. Reverse the probes on the contacts, the meter should jump again. If it doesn't jump, it's bad. (jump means an analog meter needle will move across the scale and back to the starting place) (a digital meter may have a capacitance setting, that is a good way to test condensers...discharge the cap first)

__________________
mike k
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#3

Re: Condenser Testing

10/30/2011 12:46 PM

Or simply, connect the capacitor to the net through a safety switch of the relevant amperage and measure the current drawn. Note that start (electrolythic) capacitors may only be connected to the net for 1 or 2 seconds.

In 50Hz net

current, +/- 7% (of a good capacitor) = its capacitance/14. (About 2,5A in your case)

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#4
In reply to #3

Re: Condenser Testing

10/31/2011 1:48 AM

I forgot to mention that the divider 14 is for 230V 50Hz.

For other voltage/freq. the number should be found experimentally.

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

mike k (1); PWSlack (1); Yuri B. (2)

Previous in Forum: Fire Protection of Power Transformers   Next in Forum: induction heating

Advertisement