Can you be a little more specific as to what is being injected? Assuming you mean 'secondary injection', it is a convenient way to test the health of the protection system...one injects an appropriate current into the input of the protective relay as if the CTs were delivering that current into it. This way, if the CTs are say 5000/5, you need to apply only 5A into the relay as opposed to 5000A in the Circuit Breaker's main contacts.
Is this what you meant?