Slip Ring Motor Current When Used With VFD.

11/05/2011 4:10 AM

Last week , I have installed 75 kW AC drive on 55 kW slip ring motor by shorting the slip rings, for Fly wheel mechanical press application. Everything is fine but with this configuration motor is drawing current about 67 to 72 Amp, which was 45 to 50 Amps when slip ring motor was used without AC drive.

Can anybody pls give the possible cause of it.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Slip Ring Motor Current When Used With VFD.

11/05/2011 11:20 AM

Where are you measuring the current? before or after the starter.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Oct 2011
Posts: 4
#2

Re: Slip Ring Motor Current When Used With VFD.

11/05/2011 1:10 PM

Operationally, you would get much better speed control. The slip ring motor (actually a wound rotor motor) is not really a speed regulating device but rather a torque regulator. No doubt, you have found that, even with lots of resistance in the rotor circuit, at light loads or no loads, the mill will run up to full speed. This will not happen when running on a VFD. I don't see any reason why a properly selected VFD wouldn't work on this application. You would have to size it by peak overload amps, not hp or continuous running amps.

Regards,
Xing

__________________
Taper Roller Bearing XLB.cc
Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#3

Re: Slip Ring Motor Current When Used With VFD.

11/06/2011 6:47 AM

In case of E.O.T Cranes we used fit slip ring motors for various drives. After arrival of VFD we were using Squirel Cage motors with VFD. This has resulted in cost saving as Sq.Cage motors are cheaper than slip ring motors. May i know why you went for VFD for slip ring motor as could have controlled the speeds with this motor?.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#4

Re: Slip Ring Motor Current When Used With VFD.

11/06/2011 3:06 PM

As Tony said where are you measuring the current and are you using a clippon ammeter to measure it?

If you are using a clippon ammeter an measuring the output of the drive that is normal, try using the display on the vsd to display the current, you should get a better result.

Or put your clippon on the line side of the VSD and measure from there.

Cheers

Joe

Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#5

Re: Slip Ring Motor Current When Used With VFD.

11/06/2011 4:06 PM

If the applied voltage and frequency and the load is the same as before then the motor current should be quite similar to before. What is the supply and how does this compare to the motor rated voltage (assuming frequency is matched, of course. If the motor current is higher (see other threads for verification and confirm) then there can only be a couple of reasons

1. The applied voltage is higher

2. The load is greater (or work done is higher)

Are you operating at the same frequency / speed? If not, a lower speed may mean your stored energy in the flywheel is less and thus the motor slows more now when under load demanding extra current in this part of the cycle. If it's a higher speed the power requirement goes up and the voltage may not be able to so current increases.

Another possibility is if the VFD does not have it's 'slip compensation' set to zero and is 'fighting' the speed loss when pressing causing extra current again.

If you can supply better details it will be easier to suggest what's happening.

__________________
Something new every day!
Register to Reply
Associate

Join Date: Nov 2008
Posts: 31
#6

Re: Slip Ring Motor Current When Used With VFD.

11/07/2011 3:11 AM

Output current of the drive shown in drive parameter and the current measured with the meter at drive O/p terminal is matching.

This press application is running on 50 Hz all the time.

At the time of actual punching current goes to 72 Amps, otherwise it is 67 Amps.

Customer is not ready to change the existing slip ring motor hence not going for squirrel cage motor.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Slip Ring Motor Current When Used With VFD.

11/07/2011 2:07 PM

A potential pitfall is where you short the rotor windings. If you short them on the stationary side where it is easier, the rotor power still must go through the rings and brushes, which means any arcing or resistance in the connections from wear and tear becomes a serious problem with regards to the interaction with the VFD on the stator. So it is highly recommended that the rotor windings be shorted ON THE ROTOR. But that sometimes means having to re-balance the rotor and most people don't want to go through the expense and down time of removing the motor and sending it in to a motor shop for that. However, that could be what you are seeing here if you did not.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**