Power Supply Tripping

11/05/2011 4:13 AM

I have a 3 phase 400vac power supply whose input is a 4 wire three phase 400ac while output is 3 phase 4 wire variable 400vac. when three phase inputs are supplied to power supply ,everything is fine .but as soon as the input neutral of power supply is connected ,then main input breaker of power supply trips. looking for help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Power Supply Tripping

11/05/2011 10:41 AM

Are you sure it is intended to have the neutral connected to the line side? Do they provide a terminal for it that specifically identifies it as a neutral connection, not PE? Assuming this is a solid state voltage controller, I've never seen one for 3 phase output where the incoming neutral would be of any value. Usually if you want a 4 wire output, you use a transformer on the output side that will recreate a new neutral with reference to the new variable voltage 3 phase output. Carrying a common neutral through the unit with different voltages on either side would be difficult to imagine.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Power Supply Tripping

11/05/2011 11:31 AM

I give up, it's the path of least resistance!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#3
In reply to #2

Re: Power Supply Tripping

11/05/2011 1:40 PM

The input cable is a 4 wire cable of red,yellow,blue and black wires.so it means the black wire wil be neutral.same color output terminals are available at output side.it is the old type transformer type power supply not a solid state supply

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Power Supply Tripping

11/05/2011 2:50 PM

Maybe the color code was different where the power supply was manufactured? For instance, what if blue = neutral?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#5

Re: Power Supply Tripping

11/05/2011 10:54 PM

Why Connect Neutral at all?

3 phases take care of any/all unbalance .

mm

Register to Reply
Associate

Join Date: Oct 2011
Posts: 25
Good Answers: 1
#6

Re: Power Supply Tripping

11/06/2011 1:19 AM

Do you have loads that go to neutral?

Register to Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#7

Re: Power Supply Tripping

11/06/2011 3:45 AM

When the neutral is not connected, is there a voltage seen on the terminal where the neutral should be connected? If so, you have a fault on one of your circuits after the incomer!

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: Power Supply Tripping

11/06/2011 5:41 AM

Most 3 phase loads do not require neutral. Neutral is basically only needed when single phase loads are needed.

You need to use a voltmeter and to identify 100% the phases and neutral/ground from each other. Measuring phase to neutral will show half the voltage as that from phase to phase.....do be very careful, these are killing levels......

On thinking about it, the black wire will most probably will be ground........R Y & B are generally the phases in my limited experience of AC NATO warships.....

Connecting ground to the wrong place will cause a ground fault condition that will trip any proper working breaker that senses ground faults (a good thing to have!).....exactly the problem you seem to have....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Oct 2011
Posts: 25
Good Answers: 1
#9

Re: Power Supply Tripping

11/06/2011 10:26 AM

GE picked up where I was going with my question about loads to neutral. If all loads are 'phase to phase' (single phase), or three phase, this becomes very easy to trouble shoot. Help us to help you.:)

Register to Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#10

Re: Power Supply Tripping

11/07/2011 8:31 AM

Do you only have 3 phase stuff where you are? How about lighting and single phase sockets? Do these have there own breakers? If so, are they single pole or double pole? With only the 3 phase breakers on and all the other breakers off, do you still have the breaker tripping with the neutral connected?Do you have a photograph of your Board opened up so we can get a better idea as to what is going on inside?

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#11

Re: Power Supply Tripping

11/07/2011 11:07 AM

I have a 3 phase 400vac power supply whose input is a 4 wire three phase 400ac while output is 3 phase 4 wire variable 400vac-------------------

We all missed this Prime Suspect VARIABLE

The last reply spells out what is essential for continuity of discussions .

looking for help;

You can Help with a Circuit diagram and photos as suggested.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12
In reply to #11

Re: Power Supply Tripping

11/07/2011 5:49 PM

"We all missed this Prime Suspect VARIABLE"

Speak for yourself, I caught it the first time, but asssumed it meant it was an SCR type voltage controller, which is apparently incorrect.

So coolyar if "it is the old type transformer type power supply" does that mean it is a 3 phase variac, kind of like this?

If so, are you sure it was originally designed to have a 4 wire input?

If so, I'm kind of leaning towards Tornado's suggestion that your color scheme may be off. All these are is a series of autotransformers with a wiper. Any neutral connection should go from one side to the other.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply