Transformer at VFD (AC Drive) Output

11/07/2011 3:46 AM

Can transformer be connected at Output of the AC drive?

This is basically required for the AC motor test bench at various voltage ranges line 230,415,460,575,690V, and also at various frequencies.

Pls comment.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Transformer at VFD (AC drive) Output.

11/07/2011 10:42 AM

For test bench purposes then yes, no problem. For permanent installations you have to be concerned for the transformer design because of the potential for high losses and / or saturation. You can ask a transformer mfr to make a transformer for you to address those issues however if that is a concern for your test procedure, for example if you need to guarantee efficiency.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#2

Re: Transformer at VFD (AC drive) Output.

11/07/2011 9:41 PM

I dont believe the output of a AC Drive is pure sinusidal, not sure how that will behave on the transformer, if you have 690v available on your step up transformer, possibly that can be your input to your drive(depending on your drive), then use your drive to vary the output voltage depending on what you need or vary the voltage on the variac.I am no expert ,but on a test bench with all the necessary safety in place I see no harm.

Register to Reply
Commentator

Join Date: May 2009
Location: Centurion, South Africa
Posts: 87
Good Answers: 5
#3

Re: Transformer at VFD (AC Drive) Output

11/09/2011 11:17 AM

Yes,

it can be connected, but you must remember that the output of a vsd (V/f ratio) is determined by the vsd and not adjustable. In order to keep the flux in a motor constant the vsd will adjust the output voltage in relation to the frequency output set point.

So to use it for the motor test bench at different voltages can't be done unless you require a different frequency at each voltage

__________________
R T F M .......
Register to Reply