Anonymous Poster #1

What is Cable Size for Induction Motor 30 kW Delta Star?

11/07/2011 3:19 AM

data of name plate:

pn=30kw , f=50 hz , in=64 A , vn= 380 volt

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: what is cable size for induction motor 30 kw delta star ?

11/07/2011 3:45 AM

It depends. 64A x 1.25 = 80A.

For 30°C (86°F) ambient and 3 conductors in conduit or cable:
60° wire #3 AWG, 75°C or 90°C wire #4 AWG.

For higher ambient temperatures, or more than 3 conductors in a conduit or cable, additional factors apply, which may require larger sizes.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: what is cable size for induction motor 30 kw delta star ?

11/07/2011 3:51 AM

Refer BS7671-May be 16mm^2 for short run up to starter and 6mm^2 from starter to motor.

__________________
pnaban
Reply Score 1 for Off Topic
Anonymous Poster #2
#3

Re: What is Cable Size for Induction Motor 30 kW Delta Star ?

11/07/2011 9:00 AM

As in your question For 30 kw motor , line current 64A . For star delta , six number of cables requires from starter to motor . So current in each cable will be 64/1.732=~35A . So if you use AL CABLE ,then cable size will be 35 sq mm . For copper 16 sq mm . Above cable sizes are applicable up to 50m distance.

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: What is Cable Size for Induction Motor 30 kW Delta Star ?

11/07/2011 10:02 AM

→British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: What is Cable Size for Induction Motor 30 kW Delta Star?

03/12/2024 10:47 AM

Any qualified local Electrician can sort that out. Open a dialogue. Telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); pnaban (1); PWSlack (2); Tornado (1)

Previous in Forum: Back EMF...   Next in Forum: Transformer at VFD (AC Drive) Output

Advertisement