Current Transformer

11/08/2011 6:16 PM

I have 3 HV current transformer's which have failed.They will be getting replaced with exactly the same CT's.I believe after installation of the new CT's a round of tests should be preformed (ie Ratio , polarity , secondary resistance , mag curve , primary & secondary insulation resistance and HV test of primary at power frequency) as these CT's could of been damaged in transport.

Can anyone confirm this?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Current Transformer

11/08/2011 8:58 PM

Yes! I do confirm that a series of pre-commissioning tests are mandatory for any equipment. For CTs, I would suggest:

i) IR Value (Pry to earth, each secondary to earth, pry to each secondary and between secondaries)

ii) Polarity (of each secondary)

iii) Secondary winding resistance (of each secondary)

iv) Excitation charectersitics (Mag-Curve)

v) HV Test

vi) Ratio

And compare the results with the manufacturers' test certificate to enusre that there are no damages during transit.

Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2011
Posts: 16
#4
In reply to #1

Re: Current Transformer

11/08/2011 10:59 PM

Thanks for your input

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #1

Re: Current Transformer

11/08/2011 11:42 PM

Please give or quote the relevant BS/IEC for these tests and the test voltages recommended.

__________________
pnaban
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#11
In reply to #5

Re: Current Transformer

11/10/2011 5:25 AM

IEC 60044

__________________
BNDas
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: Current Transformer

11/08/2011 9:01 PM

I don't think you need to check all these functionalities to verify the damage during transport. The transport damage is generally happen due to shock or mishandling. You can see this sort of damage just by physical looking. You can do the insulation test and the continuity check for both primary and secondary. It is very unlikely that the transport damage alters the CT ratio, polarity, magnetization curve etc. However, if you do the test for other reason, then it is a different story.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Active Contributor

Join Date: Nov 2011
Posts: 16
#3
In reply to #2

Re: Current Transformer

11/08/2011 10:58 PM

Yes I do agree it is unlikely there would be any damage in transit but it's all about covering your backside.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#6

Re: Current Transformer

11/09/2011 11:24 AM

Any idea why the old transformers failed? I would be hesitant to replace any three failed parts with identical units without an understanding of the cause of the failure.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Current Transformer

11/09/2011 11:57 AM

One possibility is that they had been open-circuited and the insulation failed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#8
In reply to #7

Re: Current Transformer

11/09/2011 12:35 PM

Yeah, that's one possibility. There's also the possibility for miswires or the infiltration of moisture. Then we can also go into the realm of plausible yet absurd. "Our welder will never cut open a transformer again. He's very sorry." A lightening strike would more than likely toast something else, too. But accurate predictions of what a lightening strike will toast is virtually impossible. I'm sure others here can come up with many more possibilities.

I'm just apprehensive about three identical failed components being replaced without an understanding of what went wrong.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Current Transformer

11/09/2011 12:42 PM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#10
In reply to #6

Re: Current Transformer

11/09/2011 2:18 PM

I agree totally with redfred . It is the correct practice to check the cause for failure before replacing the new one. If the failure was due to any fault it can damage the newly replaced CT also.The probable cause may be open circuit CT.

Reply
Active Contributor

Join Date: Nov 2011
Posts: 16
#13
In reply to #6

Re: Current Transformer

11/18/2011 4:34 AM

The reason the CT's are being replaced is they are cracking and the internal brass sleeve on each CT is slipping down.

Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#14
In reply to #13

Re: Current Transformer

11/18/2011 5:35 AM

Whoa! This is an interesting piece of information that needs to be more fully explained. It sounds like a teardown is in order, or was one made? Maybe a photo or two? Also, we need to know the type of CT, manufacturer and model numbers.

__________________
Thanks, Win
Reply
Active Contributor

Join Date: Nov 2011
Posts: 16
#15
In reply to #14

Re: Current Transformer

11/27/2011 8:55 PM

Sorry don't have name plate with me at the moment but the CT's are 11KV.

Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#16
In reply to #15

Re: Current Transformer

11/28/2011 11:34 AM

Thanks for the photo.

OK, now I'm clearly out of my league - I can't even tell what I'm seeing. That can't be a brass ring next to an 11kV bus bar?

You said something about an "internal brass sleeve?"

__________________
Thanks, Win
Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#17
In reply to #16

Re: Current Transformer

12/02/2011 11:57 PM

(as used for damping magnetic collapse in solenoids)

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#12

Re: Current Transformer

11/10/2011 9:28 PM

First, we have to say it's highly unlikely that you were sent three defective transformers. Yes, it could happen, but it's not likely (if the supplier was sending out severely-defective parts, he'd be called out on it really fast, and it would stop).

It's more likely that you might have somehow damaged the transformers.

There are two possibilities. One is the transformers aren't defective at all, and your test is defective. The second is that you have damaging them.

How does one damage a current transformer? Not from over current. They saturate and are happy enough, even if you aren't happy with what they say they see. How about over-voltage? Yes, damaged insulation. Gonzo. That can happen if you run the current transformer with a modest or high current, but without an adequately-low-resistance load. The secondary sees too high a high voltage and breaks down. End of story.

__________________
Thanks, Win
Reply
Reply to Forum Thread 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (1); biswanath.das (1); electricalexpert65 (1); JJJ (4); msamad (1); pnaban (1); PWSlack (2); redfred (2); V.I.Abraham (1); Winfield Hill (3)

Previous in Forum: Industrial/Manufacturing Engineer   Next in Forum: Conveyor Start/Stop

Advertisement